I have ongoing issues with ATS 501 by Parallax Power Supply on my '96 270.
It was installed on 11/15/2012 so it is almost 4 years old. PO warned me it takes time to have it switch from generator power to shore power.
When I use generator power, then it takes long time to transfer to shore power when I turn off generator.
Also my coach losing power time to time and when my coach lose power (115v) I feel the click (electro-magnet relays in the box)
when I run my front A/C so I turned off A/C and wait for couple of minutes then power came back.
So far ok, but it is very frustrating losing power time to time. Shore power is fine.
No breakers are tripped at all in fuse box. I think my ATS 501 unit is having problems....
Right now it is 110v. I was wondering if ATS 501 would go off when it is under 110v? Sometimes I feel like bypass that box and have shore power line connect directly to the line that goes to the fuse box.
Should I go buy another ATS 501 or what? I see it cost $250 plus shipping at Amazon.
Good thread here about ATS problems, removal hints, and one possible alternative:
Transfer switch questions (http://www.foreforums.com/index.php?topic=26766.msg216577#msg216577)
OR, if you decide to replace existing unit:
Parallax ATS503 50 Amp Transfer Switch (http://www.bestconverter.com/Parallax-ATS503-50-Amp-Transfer-Switch_p_124.html#.V5N8WmOMCuU)
Jamie,
No, the transfer switch will not cut off because of voltage below 110 VAC. Guess there is a voltage at which it would cut off, but WAY below where you would damage A/C's, etc.
Most ATS's have built in timers when switching power sources. Some are owner settable. Pull out the owners manual or get the manual on-line to find out if yours can be adjusted.
Another suggestion: With shore power off, inverter off, generator off, remove the lid to the ATS. Check that all connections are tight and not burned. Carefully look at the points of the switches to make sure they are not burned. As with any "switch", transferring under heavy load WILL arc and burn the points.
That Blue Sea manual switch is NICE.... That will do.
Hmm I see ATS 503 is newer unit, replaces 501... Will stop by RV store nearby to see if they have them in stock.
Not much to adjust the ATS 501. Just a switch for timer disable switch and three jumper wires (for 35A aux capability). Good point about tighten the clamping screws. Removed the cover and did not see anything burned.
Tighten wire clamping screws (two were bit loose and one of ground wire clamp is loose) and I even checked and tighten the 50 amp power cord ends (one I use to connect to my coach shore power interface). Still have same issues of losing power and then come back in couple of minutes then again losing power and so on.
So I decide to run generator and it works fine, no power losses at all.
Right now I am working on directly connecting shore power to fuse box (running through surge and power monitoring box) bypassing that ATS box for now (using buss connectors). I am thinking of buying manual switch and get rid of that ATS.
Since generator has to turn on or off manually so it is no point having ATS box so manual switch is far much better.
Interesting that the ATS box to surge/power monitoring box is 8 gauge wire, it should be 6 gauge since we are using 50 amp.
After connecting the wires bypassing the ATS box, turned on shore power and it came on then went off. Turns out that Progressive Ind EMS-HW 50C box is cutting off the power. I have not looked at the error code, but it looks like the voltage is too low (EMS will cut power when voltage drops to 104v or below). So I turned off the EMS box (there is remote switch) and then power came back on.
It is odd because I tested the RV park electrical connection with meter and it says 114 volts (on both 50 amp and 15 amp outlets).
I have voltage meter in my coach and it says 111 volts right now.
I guess ATS box is working fine (one thing bothers me is too long time to transfer between generator power and shore power).
The power at the pole sounds like it's marginal. Without a load you're reading 114 V, but once the coach is plugged in the load it presents pulls the power down. I would not risk running an air conditioner if the EMS isn't allowing power to pass.
Has it been verified against a known? We found our power line monitor was off by a few volts compared to what our Fluke 87 read.
Jamie,
Voltage may read fine when you check the CG pedestal, but the CRITICAL ISSUE is what is voltage when you turn on large loads.
If the power company is providing the CG with 120 VAC, but the CG wiring is inadequately sized, with no load you could read 120 VAC. And with heavy load, could read 104 VAC. Very often happens when everyone else is running heavy loads, stressing the CG wiring.
So, I strongly recommend one of the digital voltmeters that you can plug into any outlet in the coach to monitor voltage as you turn on heavy loads.
Which has happened at a couple of Parks we've been at. At first, I thought it was a problem with one of my ACs. After a CB worth of damage after a surge, I bought a EMS, I rest much easier, now. ^.^d
Checking with my digital voltmeters and it is showing 104 volts off from my coach outlet and showing 105 volts off from power on pole. No wonder my EMS was cutting off the power.
It is really hot and humid and I have to run A/C, I guess I have to run off generator power bypassing shore power. Not good considering I pay for a site. :(
Checked other power pole and it is showing 102 volts, oh man. I guess it is entire park. S&H Campground off from I-70 in Greenfield, IN (near Indy).
Right now I cannot run generator anyway until we put wires back into ATS box.
There are Hughes(?)autoformers that will reduce everyone else's power on your circuit while building up yours.
At least that's how I understand they work...
Edit: just purchased the 50 amp model for our coach
Other bad news my Montague Paratrooper folding mountain bike has been stolen :(. Lucky I still have RadRover electric bike, man I am going to lock this up!
Update: Found my bike by park office, probably a kid took my bike for joyride.
Let us know (link?) how that works. I don't like a full-hook 50 amp park where I'm ALWAYS concerned about power drop & shut-down. >:D
I looked at the info on your RadRover. Seems like a real value/nice bike.
I had to mod our prodecos as the twist throttle was not easy to use as you could not use all your hand to hold on.
Went to a thumb throttle instead,
Plus changed the grips, bars and riser to make it taller and the flat grips saved our palms from bruising
Added a cave creek seat post with rubber bumpers in it
Amazon has the info and the unit.
Probably not the cheapest but convenient
It only coverts by lowering the amps to boost the volts. The park power is not affected.
How Does it Work? | Hughes Autoformers (https://hughesautoformers.com/autoformer-university/how-does-it-work/)
Ditto ^.^d I've not run mine down below 110, but I'd sure buy one should that start happening!
Bought Hughes Autoformers and they do work very well, boosting the voltage from like 108 to 118-120. Very pleased with this purchase.