Title: Roof Heat Pump Problem
Post by: Travelin' Man (RIP) on August 27, 2016, 09:47:57 pm
Our rear Penguin heat pump initially comes on, runs about 15 seconds then goes to a higher than high blower speed for about 15 seconds, then shuts off, and after the two minute delay it repeats the same sequence. After doing this three times it will continue to run normally the fourth time.

New start and run capacitors last winter,  but wife says it's been doing since before then.

Ideas anyone?
Title: Re: Roof Heat Pump Problem
Post by: Neal Pillsbury on August 28, 2016, 12:42:37 am
Our rear Penguin heat pump initially comes on, runs about 15 seconds then goes to a higher than high blower speed for about 15 seconds, then shuts off, and after the two minute delay it repeats the same sequence. After doing this three times it will run normally the fourth time.

New start and run capacitors last winter,  but wife says it's been doing since before then.

Ideas anyone?
T-Man,
More likely than not, your AC is just Freezing Up.  If the AC speeds up several times, mostly when it is first started, the refrigerant is starting to frost the condenser fins, the freeze sensor increases the fan speed to increase the airflow and remove the frost.  But, if it frosts up too much, it shuts the AC down completely.  A sure indication is if when the AC is shut off, a bit of water sometimes drips from the intake filter grill area. 

What can cause the frost/freezing?
  4. RV AC's have more cooling capacity per unit volume of cooled space and are therefore capable of freezing up the evaporator fins more readily than a normal house air conditioning system would be.

What can you do?
[/list]

There are other things that your freezing up might be, but 95% of the time its one or more of the above and just operator misunderstanding of how an RV's AC works (they work the same as a house but the RV "house" has different volume and moisture characteristics).

What other things might be causing the freezing up — the other 5% possibility?
[/list]

Try the above possibilities first though, because it will save you bunch in parts, labor and frustration.

HTH,
Neal[/list][/list]
Title: Re: Roof Heat Pump Problem
Post by: Travelin' Man (RIP) on August 28, 2016, 01:53:02 am
Thanks Neal.

I'm aware of some of the info you just posted concerning frost but don't understand how that can occur within 15-30 seconds after initial start-up??

I have had the units drip water as you described but only after they ran continuously for a long time.

Also, I can't change the fan speed when it is running in COOL mode, only when the FAN ONLY mode is selected.
Title: Re: Roof Heat Pump Problem
Post by: Old phart phred on August 28, 2016, 03:50:51 am
Very weird indeed, doesn't sound like a condenser fan failure or a compressor going off on thermal overload. The fact that it starts and runs on the fourth attempt is very strange. Is air coming out the grilles on the first few attempts. Something wirng  heating up and finally making good contact may be a culprit. If a plastic evaporator fan set screw was loolse it might be possible for it to engage after awhile of spinning on the shaft and heating up. Idk
Title: Re: Roof Heat Pump Problem
Post by: Travelin' Man (RIP) on August 28, 2016, 08:39:51 am

Yes. It seems to run normally until fan speed
increases and then it shuts off.
Title: Re: Roof Heat Pump Problem
Post by: stump on August 28, 2016, 09:54:36 am
I would suspect the potential relay
Know Your Potential Starting Relays (http://www.achrnews.com/articles/92424-know-your-potential-starting-relays)
Troubleshooting The Potential Starting Relay (http://www.achrnews.com/articles/90387-troubleshooting-the-potential-starting-relay)
Title: Re: Roof Heat Pump Problem
Post by: Travelin' Man (RIP) on August 28, 2016, 10:18:30 am
I would suspect the potential relay.

Looking at my wiring diagram I see a PTCR
located between the start and run capacitors...... would that be it? 

Also,  regarding my initial post I was mistaken in that the fan runs on low and high as it should, and when first trying to start it runs on low, then goes to high, not higher than high.
Title: Re: Roof Heat Pump Problem
Post by: stump on August 28, 2016, 11:14:05 am
Yes.
If the relay failed it will keep the start winding energized, the compressor will cut out on thermal overload as it cools it will start again and keep repeating. It can also at times work as it is supposed to wich sounds like what yours is doing.
These replacements have more terminals than yours probably does but you just use the ones you need. This is what I put on mine when it went bad.
SUPR Universal Potential Relay - CSH Electric Motor Supply (http://www.cshincorporated.com/supr-universal-potential-relay/?gclid=CjwKEAjwl4q-BRDtzJmSk-uGunkSJACmCOY-xRvXssnhSI2TpLQa_YUbpjxYfNqvdcUWHv433OjE8hoCK-bw_wcB)
Title: Re: Roof Heat Pump Problem
Post by: Travelin' Man (RIP) on August 28, 2016, 02:35:11 pm
Many thanks!