Title: Voltage swings
Post by: Jet Doc on March 06, 2017, 10:43:18 pm
I searched the forum and cannot find a suitable answer so here goes.  I noticed last summer while traveling in August (HOT).  Gen running going down the road.  Both roof AC's running to keep cool.  After a few hours I get a fault light on the inverter control panel and voltage is varying quite a bit.  By this I mean the volt needle on the inverter control panel is waving back and forth like one of those solar powered sunflower toys.  The movement of the needle is constant.  The voltage varies between 110 and 120ish volts.  I shut off AC's power down gen for a few minutes...by then the dash air has lost the battle and we begin to glow.  Restart everything and all is well...for awhile.  The process repeats every few hours.  I have seen similar events on shore power when consuming "too much" power.  (Both roof airs, oven on etc.)  I can only assume it is temperature related, maybe the temp of a componant?  Probably a lousy connection somewhere, but where to start?  Sorry if this is in another thread that I could not find. 
Title: Re: Voltage swings
Post by: Caflashbob on March 06, 2017, 11:44:49 pm
Our coach had bad fuel lines and the resulting vacuum leaks caused fuel starvation. 
Title: Re: Voltage swings
Post by: Chuck & Jeannie on March 07, 2017, 07:54:50 am
Mike,

Does the problem also occur when you are just running one A/C unit, or only when both units are running?

The generators on Foretravel coaches are generously sized - normally, running both air conditioners won't overload them.  To function properly, the generator (electrical section) must be powered at a constant rpm by the engine.  So, first place I would check is the engine.  How long has it been since serviced?  Air cleaner fairly fresh?  As noted by Bob, any interruption in fuel flow (dirty fuel filter, leaks in fuel line) could cause erratic engine rpm, and erratic generator output.  There is a mechanical governor on the engine that maintains a constant rpm - perhaps something there not right?

If the engine is running smoothly, rpm is not fluctuating...then you will need to look at the electrical side.  Voltage regulator?  Wiring connections (power and ground)?  The generator output passes through the ATS before going to your electrical panel - does the ATS seem to switch back and forth from shore power to generator properly?

The voltage on our coach (when running generator) will sometimes fluctuate with varying loads, but never to the point of causing a power interruption.  This condition seems to come and go, and I've never determined what causes it.  So, when you do find the root of your problem, I will be interested in the solution.
Title: Re: Voltage swings
Post by: amos.harrison on March 07, 2017, 08:01:02 am
When my generator showed these symptoms, I replaced the generator voltage regulator.  Problem solved.
Title: Re: Voltage swings
Post by: nitehawk on March 07, 2017, 09:20:24 am
I would start at the simplest, least expensive possibility. Clean and snug all connections first. Then, if that didn't correct the problem proceed to check the generating source and the controls for malfunction.
Title: Re: Voltage swings
Post by: FourTravelers on March 07, 2017, 09:40:37 am
If this is happening only when running the gen set then the first thing I would check is verify the engine rpm is constant. If it also happens on shore power? Then start your checks on the electrical side, first common point being the transfer switch.

The rythmic motion of the volt meter sure sounds like a generator governor issue.
Title: Re: Voltage swings
Post by: John Duld on March 07, 2017, 10:35:14 am
Mike,
If you are running the generator going down the road for air conditioning, why is the inverter on?
What does the coach (generator) AC voltage do when the inverter AC voltage starts to move around? Can you look at both voltages or are you looking at the coach AC (generator or shore power) voltage only ? Also what does the coach voltage look like when this problem happens while on shore power?
You say you have the same problem on generator or shore power, so that would lead me toward the inverter IF you are looking at inverter voltage.

Title: Re: Voltage swings
Post by: wolfe10 on March 07, 2017, 11:15:56 am
If the generator is running, whether the inverter or inverter/charger is on or off makes no difference.

The inverter merely "passes through" voltage from the generator (and activates the charger function of the inverter/charger as well).

Same on shore power-- when the inverter or inverter/charger "sees" 120 VAC from any source, it merely passes through that power-- it does NOT invert.

And as to the comment about "is generator RPM steady":  Absolutely, this is true for fixed RPM (generally 1,800 RPM) generators, but is NOT true for those with newer variable speed (speed based on load) inverters.  Again, very different animals.
Title: Re: Voltage swings
Post by: John S on March 07, 2017, 11:25:22 am
I would look first to the voltage regulator.
Title: Re: Voltage swings
Post by: FourTravelers on March 07, 2017, 11:52:34 am
Quote from: wolfe10 link=msg=264106

And as to the comment about "is generator RPM steady":  Absolutely, this is true for fixed RPM (generally 1,800 RPM) generators, but is NOT true for those with newer variable speed (speed based on load) inverters.  Again, very different animals.

If he has a 98 U270 ? The original generator would be a fixed RPM generator correct?

Fluxuating rpm could be caused by a fuel supply problem, governor problem or voltage regulator problem to name a few.
Title: Re: Voltage swings
Post by: John Duld on March 07, 2017, 11:58:15 am
Yes the volts pass through. I'm just one of those guys that if I'm not using it I turn it off. Guess it really doesn't matter.
He says he also has the problem on shore power. I wonder is that with the generator still running or shut down?
I don't remember if the generator or shore power has priority. If shore power has priority then that would eliminate the generator voltage regulator. If the generator has priority then would look toward the regulator.
However he could have more than one thing wrong.You can live with something until it becomes more obvious when more goes wrong. Then diagnosis is more difficult.  These voltage regulators do become erratic as they age.
I think this trouble shooting boils down to does he have this problem on two different power sources or not.
Title: Re: Voltage swings
Post by: wolfe10 on March 07, 2017, 12:00:16 pm

I think this trouble shooting boils down to does he have this problem on two different power sources or not.

Totally agree.
Title: Re: Voltage swings
Post by: Jet Doc on March 07, 2017, 06:47:48 pm
Thank you for all of the replies.

1).  Gen runs smoothly with no RPM flux and gets regular service
2).  Chuck it does seem to switch between shore and gen as it should...shore power has priority.
3).  John it is the coach AC meter that fluctuates the inverter voltage is steady I think.  That is to say I have not noticed it moving around.
4).  I have seen the voltage less than steady on shore power as well.  Not as bad as on gen and I cannot remember getting the fault light on the inverter control panel unless I start the big motor while plugged in.  That will throw the fault light almost every time.  Probably a seperate issue.
Title: Re: Voltage swings
Post by: John Duld on March 07, 2017, 08:30:28 pm
Mike,
As others have said, sounds like the generator regulator could be the problem.
Like other operators have solved this problem with a new regulator hopefully it will help you.
Some of them cost more than others. Hope you have the less expensive one.
JD
Title: Re: Voltage swings
Post by: MAZ on March 08, 2017, 04:29:52 pm
Mike,
  I had a bad battery isolator that was giving me a fault on the inverter panel when the engine was running. Not sure that matches your symptoms exactly.

Mark
Title: Re: Voltage swings
Post by: George and Steph on March 11, 2017, 05:24:57 pm
I am having a similar presentation on the Powerwatch needle.  No wag on shorepower.  Checking the digital readout with genset shows a variation of a few volts.  117 - 121.  The needle however was bouncing continuously from 110 or so to around 118.  However, there is no bouncing with genset except when the AC is running.  One or both.  No alarms or error messages on either the Progressive readout or on the digital.