Onan 6500 marquis.
Solid solonoid thunk, but unit will not crank.
Batteries (coach) show 13 volts
Chassis also 13.
Help?
Pull out 10 amp fuse is good, cycled breakers on side.
Did check oil, took just a tad.
Unit started right up before we left.
Title: Re: Generator will not crank.
Post by: prfleming on July 08, 2017, 08:23:20 pm
Solenoid may be corroded or dirty. Try pressing start button several times quickly, then hold.
Title: Re: Generator will not crank.
Post by: Moby on July 08, 2017, 08:31:54 pm
Solenoid may be corroded or dirty. Try pressing start button several times quickly, then hold.
Nope, lots of clicky click, no vroom vroom
Title: Re: Generator will not crank.
Post by: Moby on July 08, 2017, 08:45:52 pm
Dumb question #27.
How the heck do you operate the slide to pull the darn thing (generator tray) out!!??
Title: Re: Generator will not crank.
Post by: Caflashbob on July 08, 2017, 08:47:59 pm
not made to slide out easily
Title: Re: Generator will not crank.
Post by: Caflashbob on July 08, 2017, 08:49:48 pm
Use boost button after starting engine then fast idle  just to see if low amps.

Cabling from everything to everything.

Title: Re: Generator will not crank.
Post by: prfleming on July 08, 2017, 09:15:16 pm
Cabling from everything to everything.
With a helper, check voltage at every terminal connection from batteries to gen, when trying to crank. Sounds like you have a terminal connection that has decided to not conduct high current.
Title: Re: Generator will not crank.
Post by: Moby on July 08, 2017, 10:52:53 pm
Duh!

Pull really hard?
No latches?
Title: Re: Generator will not crank.
Post by: Moby on July 08, 2017, 10:55:41 pm
Use boost button after starting engine then fast idle  just to see if low amps.

Cabling from everything to everything
Attempted boost trick.  No go.
Will check voltages later.  I see I need to pack a volt meter.
Title: Re: Generator will not crank.
Post by: AncloteJoe on July 08, 2017, 11:07:44 pm
if the voltage is good, then the starter may be going bad. check the connections to the starter as well. make sure they are clean and tight with no corrosion. 
Title: Re: Generator will not crank.
Post by: Moby on July 08, 2017, 11:24:17 pm
Dry camping at a Wal-Mart for the night.  Will figure out things in the am, or when I get a volunteer and a volt meter.
Worse yet, their coolers are down, and no cold adult beverages available!
THE SHAME OF IT ALL!
Title: Re: Generator will not crank.
Post by: Caflashbob on July 08, 2017, 11:40:31 pm
Disconnect exhaust system then use a fork lift to support the gen as you slide it out.  Cabling may need unhooking
Title: Re: Generator will not crank.
Post by: TulsaTrent on July 09, 2017, 12:27:48 am
Dumb question #27.
How the heck do you operate the slide to pull the darn thing (generator tray) out!!??
Mine has a bolt on each side at the bottom. If you do not remove those, you will  have to pull really, really hard!
 
Trent
Title: Re: Generator will not crank.
Post by: saddlesore on July 09, 2017, 01:28:48 am
Try giving the starter a good whack...... bendex or solenoid may be stuck
Title: Re: Generator will not crank.
Post by: John S on July 09, 2017, 08:00:54 am
Wal mart has volt meters sometimes in their hardware section of tools.
Title: Re: Generator will not crank.
Post by: wolfe10 on July 09, 2017, 10:28:42 am
Reach up from under the generator and use a long screwdriver, etc to prying gently on the fan blade,  to turn over the generator-- just to confirm that the motor is not locked up.

Next, check voltage between large positive lug on the generator to good clean metal on the generator both before and while cranking.  Then check between the positive lug and good clean chassis metal as a ground.  The second test to determine if the ground path is the problem (the bearings of the generator slide IS the ground path, and not a great one). 

Let us know what you find.
Title: Re: Generator will not crank.
Post by: Mike Leary (RIP) on July 09, 2017, 10:36:27 am
Do let us know, that's the same ultra quiet unit we have. Give us the hours after you find some cold beer!  ^.^d
Title: Re: Generator will not crank.
Post by: prfleming on July 09, 2017, 11:31:57 am
Attempted boost trick.  No go.
Will check voltages later.  I see I need to pack a volt meter.
Also recommend packing a clamp-on DC current meter. Here are some more ideas:

- Clamp current meter on the large 12V cable to generator, try cranking, a high current (say 100+ amps) and no crank will indicate a locked generator or starter. If reading only small current for solenoid (say under 10 amps), then more checking for bad connections...

- Another way to test Brett's idea of a bad ground is to measure voltage between the generator frame and a good clean point on the coach chassis while trying to crank. There should be NO voltage, if ground is flaky there will be measurable voltage between generator frame and coach chassis.
Title: Re: Generator will not crank.
Post by: Racedad on July 09, 2017, 11:32:34 am
If you jump across the solenoid and it cranks the solenoid is bad. If you can use jumper cables from a good battery (toad?) to the side of the solenoid going to the starter and it doesn't crank the starter has failed. If both of the tests fail you don't have enough amps from the coach/generator battery. Just checking the voltage will not tell all if it is not checked when trying to start. Hope this helps.
Title: Re: Generator will not crank.
Post by: red tractor on July 09, 2017, 08:33:47 pm
If you find the solenoid is bad make sure that you get an Onan solenoid. There will be a part number on the Onan solenoid and no a Ford starter solenoid is not the same.
Title: Re: Generator will not crank.
Post by: Moby on July 09, 2017, 11:13:43 pm
All great suggestions.  Please keep them coming.  Currently at a camp in Old Mystic, running off shore power.  Will be home tomorrow with my tools and testers.  Intend to keep you all updated
This shake down cruise has taught me a couple of things:
1)  It's not IF things go wrong, its WHEN they go wrong.
2)  gonna need a bigger tool kit.
Title: Re: Generator will not crank.
Post by: Michaelther4 on July 10, 2017, 12:54:26 pm
Try moving around the fuse holder while trying to start it.  My fuse checked out good, but the fuse holder was bad, when I moved it around it made a connection and started. Let us know what you find.
Title: Re: Generator will not crank.
Post by: Moby on July 10, 2017, 03:55:50 pm
Try moving around the fuse holder while trying to start it.  My fuse checked out good, but the fuse holder was bad, when I moved it around it made a connection and started. Let us know what you find.
Michael, in your case, did the unit crank?
When I pulled my fuse and holder it did nothing.
Title: Re: Generator will not crank.
Post by: Michaelther4 on July 10, 2017, 10:37:04 pm
Yes in my case it was cranking.
Title: Re: Generator will not crank.
Post by: Moby on July 16, 2017, 06:39:16 pm
Ok.
I give up.
Managed to do some voltage testing.
13.6 positive lead to generator body, 13.6 positive lead to chassis.
13.5 when cranking.
At a camp tonight, went to show a neighbor what was going on, and she starts right up.
Go figure.
Title: Re: Generator will not crank.
Post by: wolfe10 on July 16, 2017, 06:44:11 pm
Did you have the same no-start symptoms when using the one switch on the generator itself VS the in-coach switch???
Title: Re: Generator will not crank.
Post by: Dakota Slim on July 16, 2017, 07:11:49 pm
Ok.
I give up.
Managed to do some voltage testing.
13.6 positive lead to generator body, 13.6 positive lead to chassis.
<<<<<<<<13.5 when cranking.>>>>>>>>
At a camp tonight, went to show a neighbor what was going on, and she starts right up.
Go figure.

I thought it wouldn't crank.
Title: Re: Generator will not crank.
Post by: Moby on July 16, 2017, 07:23:55 pm
My bad.  Attempting to crank.
Did get it to crank right over and start.  Ran for 1/2 hour, let it cool down (removed load) and shut down.
Attempted to start again and no cranky.
Title: Re: Generator will not crank.
Post by: Moby on July 16, 2017, 07:25:05 pm
Did you have the same no-start symptoms when using the one switch on the generator itself VS the in-coach switch???

All three switches gave same symptoms, but could not measure voltage.
Since it ran this evening, I'm going with the motor is not seized, Brett.
Title: Re: Generator will not crank.
Post by: red tractor on July 16, 2017, 08:16:25 pm
Sounds like a bad connection or a faulty starter motor
Title: Re: Generator will not crank.
Post by: Protech Racing on July 16, 2017, 09:38:05 pm
 Put a test light on the starter solenoid, check for good volts , bright light.  FWIW I have a 25 ft test light wire, so I can sit in the seat and check functions /watch the pretty light.
Title: Re: Generator will not crank.
Post by: craneman on July 16, 2017, 11:13:33 pm
A power probe makes trouble shooting a lot easier. They come with a 25' cord and a 25' extension, battery clips and lighter adaptor. The model I use also has a volt meter built in.

Amazon.com: Power Probe PP3LS01 Power Probe III Circuit Tester with PPLS01... (https://www.amazon.com/Power-Probe-PP3LS01-Circuit-Tester/dp/B007QV0R7W/ref=sr_1_6?ie=UTF8&qid=1500261587&sr=8-6&keywords=power+probe+3)
Title: Re: Generator will not crank.
Post by: Moby on August 10, 2017, 08:23:45 am
Sounds like a bad connection or a faulty starter motor
I apologise, its been a while since I've updated this post.  Life gets in the way sometimes.
Red Tractor wins.  It is indeed a bad starter motor.  At the shop now getting it taken care of so we can head south to watch the Sun get gobbled up.
As always, thanks for the great suggestions.