Title: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: Hans&Marjet on August 22, 2017, 11:00:05 am
Just installed new AGM house batteries after removing the old,bulging gel batteries.  Hooked everything up and got good voltage while on shore power.  When the coach was started the voltage for the house batteries starting fluctuating from 14.8-15.2.  Confirmed this with a multimeter.  Checked the chassis batteries and they were charging13.7- confirmed with multimeter.  It seems everything is working ok except the charging of the house batteries while the engine is running.

What could this be?  I am stumped by this one.

Thanks for your help
Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: Mike Leary (RIP) on August 22, 2017, 11:06:19 am
What could this be?  I am stumped by this one.

I'll put this thread back on top, as I'm curious, as well.  ^.^d
Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: John44 on August 22, 2017, 11:13:07 am
Assuming you checked all connections,what inverter/charger do you have,is it set up for the AGM batteries?Were the batteries fully charged when installed?
Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: wolfe10 on August 22, 2017, 11:21:31 am
I would start by checking voltage at the battery isolator.  Check at the center lug (from alternator B+), then at the two outer lugs that go directly to the battery banks. 

Let us know what you find.

And, assuming you do not have solar or other charge source connected to the house bank what could provide an alternate charge source at incorrect/high voltage.

Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: Hans&Marjet on August 22, 2017, 03:55:17 pm
Cleaned and checked Isolator lugs

Alt post @ 15.2
House post@ 15.1
Chassis post @ 14.2

Checked alternator output 15.7

Bad regulator...? I do not see an adjustment for v-reg

160 amp alt with 3 step 79000 (regulator) ????

Thoughts

Thx All
Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: wolfe10 on August 22, 2017, 04:01:34 pm
Cleaned and checked Isolator lugs

Alt post @ 15.2
House post@ 15.1
Chassis post @ 14.2

Checked alternator output 15.7

Thx All


Couple of issues.

Why the drop between alternator (assume B+ terminal of 15.7) and reading at the center lug of the isolator of 15.2.  That is quite a drop in that large-gauge wire.

Diode-based isolators loose about .7 VDC across the diodes, so you should be seeing that drop between center lug and house battery lug as well as the chassis battery lug.

Since the sense wire is on the chassis battery side (exact location not critical as long as it represents chassis battery voltage) and is reading correct voltage (14.2) I would look very hard at the isolator being at issue.

Again, for troubleshooting, one needs to explain why no voltage drop between isolator center lug and house battery.  As posted above, if solar or any other means of charging the house bank is active, THAT has to be addressed first.
Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: Hans&Marjet on August 22, 2017, 07:30:05 pm
Brett..I'm abit confused here....is the Alternator output voltage not to high.? was under the impression that the  output should be 14.2V..?

H
Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: wolfe10 on August 22, 2017, 11:10:29 pm
NO, alternator output should be about .7 VDC higher than you want the batteries to see, as there is that .7 VDC drop across the diodes in the diode-based battery isolator.

All those big aluminum fins on the isolator are to dissipate the heat from loosing that .7 VDC.

What you do care about is voltage on the "battery side" of the isolator, and 14.2 at the chassis battery says that part of the system is OK.

You need to find out why house bank is higher-- bad isolator? alternate charging source? other?

And, anytime you have puzzling numbers, spend 20 minutes making sure all connections at the isolator and alternator are CLEAN AND TIGHT. Could save you a lot of time and money.
Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: Neal Pillsbury on August 23, 2017, 12:59:02 am
Brett..I'm abit confused here....is the Alternator output voltage not to high.? was under the impression that the  output should be 14.2V..?
Hans, adding to Brett's help, if your readings are correct, the start battery side of the isolator is good but there is something wrong with the cable or cable to post connections from the B+ post on the alternator to the alternator post on the isolator, AND the House Battery Side of the isolator appears to be shorted.  Less than stellar Ground cable connections at the alternator and at the Start Battery bank would mess things up too.
It's always much easier to see and understand these things in person, but here goes anyway:  Just a stream of thoughts that may be of help to you in chasing this down:
From your Isolator post readings:[/list]HTH,
Neal
[/list]
Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: Old phart phred on August 23, 2017, 02:11:51 am
Does anybody know how the new Cole hershee smart isolator modulate the alternator sense voltage?
Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: Chuck & Jeannie on August 23, 2017, 08:17:37 am
Hans,

Do you have a 3-post or 4-post isolator?  On our '93 model, the (still) OEM isolator has 4 posts.  There is a jumper between the two AUX battery posts.  IF you have the same setup, could the jumper have been removed and then reinstalled on the wrong post?  If the jumper was incorrectly attached between the ALT post and the AUX battery post, that would at least explain your high house battery voltage.  Just guessing here...

In photo, isolator posts (left to right):  AUX(house) - ALT - AUX(extra) - MAIN (start)
Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: Hans&Marjet on August 27, 2017, 06:20:10 pm
Chuck....the jumper wire is OK..

Update:Not good

We still have a problem of overcharging. After cleaning the Isolator cables and connections we see the following results.

Alt V = 15.7
Isolator Alt V = 15.2
Isolator House V = 14.8
House V resting 12.8
House V running 15.2...?????? not good

Chassis running V = 13.9-14.0


Lost as to what it could be....

One question, why is the voltage coming from alt @ 15.7.....seems to high ??

Hans


Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: wolfe10 on August 27, 2017, 06:25:34 pm
Hans,
The alternator voltage is NOT your issue.  With a diode-based battery isolator, alternator output needs to be .7 VDC higher than you want at the batteries to account for power turned in to HEAT in the isolator.

House battery "running" is the problem. Could be a direct connection from isolator alternator to house lug. That would suggest an isolator replacement.

Secondary issue is still the .5 volt drop between alternator B+ and alternator lug of the isolator. That is NOT the cause of high house bank voltage, but that is way too much drop in that large-gauge wire.
Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: Hans&Marjet on August 27, 2017, 06:39:20 pm
Brett....

Sorry I had a typo

Alt V = 15.7
Iso Alt V = 15.5
Iso House V = 14.8
House V running 15.2

Hans

Hans,
The alternator voltage is NOT your issue.  With a diode-based battery isolator, alternator output needs to be .7 VDC higher than you want at the batteries to account for power turned in to HEAT in the isolator.

House battery "running" is the problem. Could be a direct connection from isolator alternator to house lug. That would suggest an isolator replacement.

Secondary issue is still the .5 volt drop between alternator B+ and alternator lug of the isolator. That is NOT the cause of high house bank voltage, but that is way too much drop in that large-gauge wire.
Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: Hans&Marjet on August 27, 2017, 06:43:33 pm
I also have these cutout switches on the house negative side..

Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: wolfe10 on August 27, 2017, 06:55:08 pm
I also have these cutout switches on the house negative side..



So, check voltage from one lug of the disconnect to the other. Said another way, see if there is significant resistance/voltage drop across the disconnect switches.
Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: Hans&Marjet on August 28, 2017, 02:57:40 pm
Update; Problem fixed....Bad Isolator on the house side...Installed 240amp unit a few cable mods but its done.

Brett,Chuck,Neal....and all,as always Thank You for the help it's truly appreciated 

Hans

Title: Re: Fluctuating Voltage 14.9 to 15.2 on house batteries
Post by: Neal Pillsbury on August 28, 2017, 09:17:39 pm
Great news Hans!  Thanks for the update and closing the loop.
See you down the road.
Neal