Title: AC Power Anomoly
Post by: RandallBrink on August 16, 2018, 07:24:15 pm
I parked in dry camp this afternoon, and started my generator for a/c. The a/c units were run on low for approx. 25 min., when they dropped off, the generator made asound like slowing down, and suddenly no AC power at all. Checked all circuit breakers, including those on the Zantrex Freedom Inverter. Nothing appeared out of place. But no AC power anywhere.

Any help would be hugely appreciated!
Title: Re: AC Power Anomoly
Post by: craneman on August 16, 2018, 07:36:43 pm
What is your fuel level?
Title: Re: AC Power Anomoly
Post by: wolfe10 on August 16, 2018, 07:52:10 pm
Did you turn off and back on the breakers on the generator itself?

And, what generator do you have?

Any problem with re-starting the generator?  Run OK?

If generator is running OK, next step would be to check connections from generator to house and then at the ATS.
Title: Re: AC Power Anomoly
Post by: RandallBrink on August 16, 2018, 08:52:35 pm
Brett, thanks.

1. Generator is Cummins Onan 7.5;

2. Gen ran fine throughout incident. I have started the genset a number of times, and it seems to run fine.

3. I can only find one pop-out type 25 amp breaker on the main face of the generator, and none in the main fuse/breaker box.

I checked all visible electrical connections between genset and inverter—there really are no visible connections—just many boxes with heavy AC wiring.
Title: Re: AC Power Anomoly
Post by: Keith and Joyce on August 16, 2018, 09:20:22 pm
First turn any breakers that you find on and off a few times.  Cannot always tell if tripped unless you do that.  Next take off cover on ATS and check for voltage on the contactor terminals.  With an INSULATED screwdriver you can manually push a contactor in but first disconnect all 120 volt supply and turn off the inverter.  Obviously have the genny running.  Be careful if you are not comfortable with electricity don't do it.

Keith
Title: Re: AC Power Anomoly
Post by: craneman on August 16, 2018, 09:23:12 pm
The power wires for the air conditioner do not run through the inverter.
Do you have an ATS switch on your model coach?
Title: Re: AC Power Anomoly
Post by: fouroureye on August 16, 2018, 10:57:04 pm
1st, turn everything off. This happened to me on my 88.... if memory serves me 200A in line breaker

In big bay to the rear of the gen set should be your electrical connections. Behind the wall they are mounted on is a round access hole. You can reach it from the smaller compartment near the water bay. In this access hole is the main reset, just push it in, you will hear the click.

Start everything up
Title: Re: AC Power Anomoly
Post by: stump on August 18, 2018, 09:54:58 am
Is your generator the same as this?
I had to replace the circuit breaker on mine it had gotten tired and lost continuity through it.
Title: Re: AC Power Anomoly
Post by: RandallBrink on August 18, 2018, 04:20:14 pm
Stump,

Yes—Identical generator. Starts and runs fine, but no electrical output, and the only circuit breakers I can find are the two main box 50a breakers. None on the generator itself.
Title: Re: AC Power Anomoly
Post by: stump on August 18, 2018, 04:22:55 pm
See the middle picture Mine has a breaker there.
Title: Re: AC Power Anomoly
Post by: RandallBrink on August 18, 2018, 04:40:45 pm
OK, the picture solved the mystery. On mine, the clearance is tight on the front, ad I couldn't see the breaker due tight dark area and wire obscuring.

The breaker is tripped (outboard) and will not remain closed upon gen start.
Title: Re: AC Power Anomoly
Post by: wolfe10 on August 18, 2018, 05:03:09 pm
With the one breaker tripping as soon as it "makes power" there are a couple of things to check.

There could be a bad connection/dead short at the generator to coach wiring, in the coach wiring to the ATS (not very likely) and at the ATS-- generator "IN" side.

I would start with those. few connection areas.

Yes, it could also be in the generator, in which case, if you disconnect generator to coach wiring it would still trip.
Title: Re: AC Power Anomoly
Post by: RandallBrink on August 18, 2018, 05:28:31 pm
Great Brett, thanks again. This gives some specific things to run down and I'm sure I can find the ground and have already located the connections for the ATS.
Title: Re: AC Power Anomoly
Post by: stump on August 19, 2018, 08:12:14 am
When you reset it does it click back in nice and firm or feel mushy? Mine felt mushy, replaced it no more issues.
Title: Re: AC Power Anomoly
Post by: stump on August 19, 2018, 09:53:02 am
OK, the picture solved the mystery. On mine, the clearance is tight on the front, ad I couldn't see the breaker due tight dark area and wire obscuring.

The breaker is tripped (outboard) and will not remain closed upon gen start.
Is everything turned off inside,A/C etc?
Turn off all 120v breakers inside coach. Reset the breaker on the generator. Start Generator . Does breaker trip? Yes/No
 If No go inside coach and start turning on breakers see which one circuit is causing fault.
Title: Re: AC Power Anomoly
Post by: RandallBrink on August 19, 2018, 12:07:37 pm
My recollection is that was mushy, not the firm snap you'd expect.
Title: Re: AC Power Anomoly
Post by: RandallBrink on August 19, 2018, 12:09:21 pm
I will do this test. When I was testing yesterday, I was not turning off the 120v breakers. Should have remembered to do this.
Title: Re: AC Power Anomoly
Post by: stump on August 28, 2018, 07:57:10 am
What did you find?
Title: Re: AC Power Anomoly
Post by: RandallBrink on August 28, 2018, 11:51:28 pm
I have not yet had the opportunity to go through the breaker test, but plan to do so tomorrow, Wednesday, Aug. 29th. Thanks, and will report findings.