Re: Solar power for storage
Reply #30 –
Craneman I have a sw 2812. Sister to your sw3012. Both use either a me-rc or the me-arc remote panels,
In the manual for either remote it shows the battery types, two different AGM profiles are in the menu,
AGM One is for your lifelines. AGM Two is for the rest,
AGM one has its max charging voltage set for the lower internal resistance Lifeline batteries at 14.3 and when the equalization process is triggered it sends 15,5 volts for four hours to your batteries
AGM two has its max at 14.5 volts and if used on lifelines will slowly damage them from overcharging,
If you try to equalize in AGM 2 nothing happens. Same 14.5 volts,
Gel profile does not allow equalizing either. Same 14.2 max volts as charging.
16 volts into a lifeline is not good,
All these voltages are based on 78 degrees and a BTMS is needed to avoid over or undercharging any battery bank.
The ME-ARC shows how many days since equalization and as it has a clock inside can be set to remind you at a future date to equalize,
Once or maybe twice a year unless a heavy continuous user or your use short cycles the batteries a lot?
Obviously 16 volts in colder weather might be ok I do not know what voltage the BTMS will have the charger send out in the AGM 1 profile if the equalize function is engaged during colder weather than the 78 degrees that is the std temp profile.
But the chart says 15.5 max so I would think the EQ voltage regardless of temp is that number?
The ARC version of the remote panel allows bulk charge reagsrdless of battery SOC and has a silent mode.
Both panels manuals are available for download.
The ARC can be reset to turn on the charger above the RC's default 80% SOC so the batteries are not running down to 80% and back up all the time. Needless cycling unless on limited power