Re: Secondary transfer switch 2001 u320
Reply #3 –
We replaced our ATS under the bed about a year ago. Kept tripping. It still would trip on occasion when we exceeded 20 amps an that #8 breaker. We replaced our inverter/converter with a Magnum MS 2812. I talked to the Tech at Magnum re: the ATS tripping and he said that there are 2 ways to eliminate this. 1. Replace the #8 breaker with a 30 amp and the feed wire. or 2. Remove that ATS and wire directly through the 2812. He advised that there is a transfer switch built into the inverter.
What follows is an email thread between me and their Tech Rep Darren Massey.
Me:
"We some times have our Charger Breaker trip. Based on the attachments of the coach wiring diagram and the Electrical Panel Breaker IDs, am I correct to assume that the 20 Amp Charger Breaker, that lives in Circuit Breaker Box #2 is powered by the 20 Amp breaker- #8 - from the Main Circuit Breaker Box? Why would the Charger Breaker trip? Would appreciate your input."
Darren:
"I would recommend using a 30 amp breaker. Our inverter/charger will use 18 amps and full charge rate which will only leave 2 amps for pass through I see you have a bypass transfer switch on the output but not sure which position is priority."
Me:
"Can I run the 6/2G power line directly to the inverter converter and then run the inverter/converter output directly to Circuit Breaker # 2 and bypass Switching Relay #2?"
Darren:
"You could do that but you will need to move the 6/2G wire from the main buss in the main panel to thirty amp breaker or wire the inverter for single in single out 60 amp and change the wire on the output of the inverter to 6/2G also. This is because the 6/2G there now is protected by a 50 amp breaker and all wire must be sized for that size overcurrent protection. FYI I would probably do this if it was my installation, one less failure point."
I have not done anything yet as the breaker is not tripping often these days.
Hope this helps.