Re: Why is my cold water hot?
Reply #8 –
Glen - check the zone valves on the AquaHot. IIRC the basement one is shared with the bathroom (controls are independent thermostats, but I seem to recall the plumbing is shared). I'm wondering if that zone valve is stuck open (usually they stick closed, but you never know - we had one in a house with hot water baseboard heating stick open). With all the zones turned off (but AH on), if you feel one pumping hot water through, that could be it.
It could also be that the knob for the thermostat is misaligned to the control shaft, and what you think is 40-45 is actually higher. But then when you turned it down all the way (ignoring where it was pointing) it should have changed the behavior.