Re: Another apparent 120VAC power problem
Reply #1 –
Trent,
As far as diagnostics, the first thing I would do is disconnect from shore power and start the generator. That will tell you (if everything now works) that from the ATS onward, all is OK. If all doesn't work, your issue is from the ATS to main breaker box.
Then, if you are safe working around 240 VAC, pull out your voltmeter.
Check CG outlet first:
Outer straights are hots
Center straight is neutral
Center round is ground.
So from either outer to either center should show 120 VAC
From outer to outer should show 240 VAC. If it shows 0, the outlet/CG is mis-wired.
If all OK there, with all power off, remove the lid to the ATS. Plug back in. Check here for power IN and power OUT.
Black and red are the hots. White is neutral. Green is ground.
If all OK, check at the main 120 VAC breaker box. Remove the 2 screws holding the cover. Check here for L1 and L2 (same colors as at ATS.
And, will need more detail on what "front furnace" you have. If a propane furnace, they are 12 VDC, not 120 VAC. So, if this is what you have, likely an unrelated issue.