LP GAS DETECTOR AND VALVE CONTROLLER

I have a 1992 Foretravel Unihome.  The LP gas detector finally died and when I took it off it was from 1991 (really old).  I saw a replacement looks flush like the one that was in my RV.  It says it fits most Fleetwood or Winnebago.  So I searched the internet for a Foretravel model of some sort.  Nothing.  The one I see is called a Safe Alert.  Catalog # 56358.  Will this work?

I appreciate your input.  Just me trying to keep my RV working good.

Thank you,

Yolanda
Rod O.
1992 U300 40'

Re: LP GAS DETECTOR AND VALVE CONTROLLER

Reply #1
I did some more reading on this.  It seems I need a Safe Alert co/propane detector  model 70-742-R-Kit to replace the old CCI controller model 7719.  The Safe Alert model says I have to replace the solenoid because it does not work model 7719.  Bummer.  Is this my only option?
Rod O.
1992 U300 40'

Re: LP GAS DETECTOR AND VALVE CONTROLLER

Reply #2
Detector: I believe that is the same detector I used to replace mine in a 95 and a 97. Probably the same as yours. It's the closest in size to the original. I had to make a little patch to completely cover the hole.

Solenoid: Many of us have either eliminated the solenoid altogether (my choice) or disabled it by removing the little pintle. Might as well replace your LP regulator at the same time.
jor

93 225
95 300
97 270
99 320

Re: LP GAS DETECTOR AND VALVE CONTROLLER

Reply #3
Had the same problem on my 96,I put a toggle switch next to the detector that way I can still turn the propane off from inside the coach plus I didn't have to fool with any piping,move the switch up for on down for off.
96 U270 BUILD 4810
85 380SL
Drummonds TN.

Re: LP GAS DETECTOR AND VALVE CONTROLLER

Reply #4
We replaced ours last year with a Safe Alert, the same as Jor's. It fit right in, but the PO had modified the housing, already. We had a hard time finding it (I think we found it in Canada!) and, yes, I think our gas guy had to do some fooling around. I don't see a model #, but I can search my files, if you need further information. We test ours with a little bit of rubbing alcohol on a rag, don't waste good whiskey!  ^.^d
1993 U-240 "La Villa Grande"..CAT 3116 w/ Pacbrake PRXB...Allison 3060 6-speed..
Previous: 1983 Airstream 310 turbo diesel, 1979 Airstream 280 turbo diesel
                                      Build # 4297
                                      PNW natives
                      Home base:  'Cactus Hug' (Ajo, Arizona)
                        DW Judy & Chet the wonder dog
                        Full-Timers 'Sailing the asphalt sea'

Re: LP GAS DETECTOR AND VALVE CONTROLLER

Reply #5
Bookmarking this one....mine is the original from 1989 and is working fine but is SUPER sensitive so I've been thinking a replacement is soon around the corner....
Jeff & Carrie
2023 Geneva 31VA
1989 Grand Villa 36' ORED "The Button Pusher" - GONE 🥺

Re: LP GAS DETECTOR AND VALVE CONTROLLER

Reply #6
mine is the original from 1989 and is working fine but is SUPER sensitive so I've been thinking a replacement is soon around the corner....
You've got your money's worth! I show ours was replaced in '03 and, as said, last year. Ours has had the solenoid removed, as well.
1993 U-240 "La Villa Grande"..CAT 3116 w/ Pacbrake PRXB...Allison 3060 6-speed..
Previous: 1983 Airstream 310 turbo diesel, 1979 Airstream 280 turbo diesel
                                      Build # 4297
                                      PNW natives
                      Home base:  'Cactus Hug' (Ajo, Arizona)
                        DW Judy & Chet the wonder dog
                        Full-Timers 'Sailing the asphalt sea'

Re: LP GAS DETECTOR AND VALVE CONTROLLER

Reply #7
I did some more reading on this.  It seems I need a Safe Alert co/propane detector  model 70-742-R-Kit to replace the old CCI controller model 7719.  The Safe Alert model says I have to replace the solenoid because it does not work model 7719.  Bummer.  Is this my only option?


Rod,

I replaced the CCI model 7719 with a Safe-T-Alert 70-742-R-Kit-BR from American RV Company RV Parts Accessories Appliances Repair & Service | American RV Company The new one has a solenoid that gets a continuous 12 volts and stays warm to the touch.  It takes about 10 minutes to reset the alarm but the solenoid is on as soon as there is power.  The detector is a 4 wire instead of three and you have to add a ground to the chassis or the negative post on the battery.  I got lucky and was able to find a good chassis ground for the black wire on one of the floor bolts underneath the drawer in the kitchen right next to the detector!  The yellow wire from goes to one of the white wires on the detector.  I connected the two red wires to the one red and the other white wire from the detector for the other connection. Using wing connectors makes it easy to remove.

I also replaced the twin site sender IP5628S02537 on the tank from Gas Equipment Company Welcome to Gas Equipment Company, Inc.  It's 0-90 Ohms and is an exact replacement.  It works perfect on the tank and with the Audit 860.  My old one was cracked and needed replacement. 

You'll have to enlarge the hole a little for the new one to fit.  I also used winged wire nuts for the connections inside,  About $250 for everything.  They should be changed every 5 years and the Safe-T- Alert will give an end of life reading. 

Jerry 
The selected media item is not currently available.
Jerry and Cindy Maddux
1993 U300/36WTBI DD6v92TA
build 4271  "Miss Lou"
1995 suzuki sidekick 4x4 toad
Gulfport, Ms

"Pride of Ownership"

Re: LP GAS DETECTOR AND VALVE CONTROLLER

Reply #8

Rod,

I replaced the CCI model 7719 with a Safe-T-Alert 70-742-R-Kit-BR from American RV Company RV Parts Accessories Appliances Repair & Service | American RV Company The new one has a solenoid that gets a continuous 12 volts and stays warm to the touch.  It takes about 10 minutes to reset the alarm but the solenoid is on as soon as there is power.  The detector is a 4 wire instead of three and you have to add a ground to the chassis or the negative post on the battery.  I got lucky and was able to find a good chassis ground for the black wire on one of the floor bolts underneath the drawer in the kitchen right next to the detector!  The yellow wire from goes to one of the white wires on the detector.  I connected the two red wires to the one red and the other white wire from the detector for the other connection. Using wing connectors makes it easy to remove.

I also replaced the twin site sender IP5628S02537 on the tank from Gas Equipment Company Welcome to Gas Equipment Company, Inc.  It's 0-90 Ohms and is an exact replacement.  It works perfect on the tank and with the Audit 860.  My old one was cracked and needed replacement. 

You'll have to enlarge the hole a little for the new one to fit.  I also used winged wire nuts for the connections inside,  About $250 for everything.  They should be changed every 5 years and the Safe-T- Alert will give an end of life reading. 

Jerry

This weekend I changed out the old Marshall 260 propane regulator for a Marshall MEGR 291 which I should have done when I replaced the propane detector. I didn't check the pressure before installing but all my gas appliances are working much better. 

I'm not sure when the regulator should be changed ( I believe at least every 10 years ) but I know the furnaces are very sensitive to gas pressure.  I have a one year old Atwood helium fridge and it was starting to take a few tries to light the burner.  Now the proper gas pressure 11" WC comes up much quicker when the main valve is turned on and the fridge lights on the first attempt.

I had to remove one of the old fittings between the main valve and the old regulator to make room for the new larger regulator but was able to use the original bracket. 
The selected media item is not currently available.
Jerry and Cindy Maddux
1993 U300/36WTBI DD6v92TA
build 4271  "Miss Lou"
1995 suzuki sidekick 4x4 toad
Gulfport, Ms

"Pride of Ownership"

Re: LP GAS DETECTOR AND VALVE CONTROLLER

Reply #9
Crud just checked my original detector that was working last week, no go. But maybe fumes from Howard's feed and wax. Will try again tomorrow. If it fails is valve normally closed and has to be powered open?
Old Phart Phred, EIEIO
89 GV ored 36' #3405 300 hp cat 3208 ATAAC side radiator, mountain tamer exhaust brake

Re: LP GAS DETECTOR AND VALVE CONTROLLER

Reply #10
I'm not sure when the regulator should be changed ( I believe at least every 10 years ) but I know the furnaces are very sensitive to gas pressure.  I have a one year old Atwood helium fridge and it was starting to take a few tries to light the burner.  Now the proper gas pressure 11" WC comes up much quicker when the main valve is turned on and the fridge lights on the first attempt. 

I bought a leak down test kit 10 years ago when having furnace issues, since then I check propane pressure every couple years or when ever I've opened a propane line.  It is not that hard to do.  I connect at stove burner and see pressure and see it holds pressure.  After it is important to test this connection with soapy water or leak detector.
97 U295 40, Build #5040, 6C8.3 325 HP
Oregon Continuous Traveler
Samsung Residential #RF20HFENBSR,
Xantrex SW2012, (3)AGM8D Hse, (2)AGM Grp24 Eng, Victron BMV-712, 1800w Solar 4 LG & 2 Sunpower
Extreme Full Body Pt w/hdlmps, new furn/floor, 4 down Lexus 2004 GX470 AWD curb weight 4,740 lbs
Prev: 1990 Barth, 10L 300 2 yrs; 91&92 Monaco Signature, 10 yrs, 10L C 300 &  6C8.3 300; 1997 ForeT 6C8.3 325 since May 2017.  Employed by Guaranty RV 14+ yrs.  Former VW New Car Dlr/Service Dlr, Sales Mgr, Rv Sales, and Service Adviser from 1968-2017
"Don't criticize what you can't understand" Bob Dylan

Re: LP GAS DETECTOR AND VALVE CONTROLLER

Reply #11
If it fails is valve normally closed and has to be powered open?
The propane solenoid safety valve fails to the closed position.  It must be supplied proper voltage to open.  See post linked below:

LP circuits help please .
1993 U280 SE 40' WTBI, Build: 4359
C8.3 300hp, 6-Speed, Exhaust Brake
960 watts on the roof (6 x 160)
Sorento (or BOLT) on a Kar Kaddy SS
"Nature abhors a vacuum"

 

Re: LP GAS DETECTOR AND VALVE CONTROLLER

Reply #12
They taught us when doing the leak down test to check it to 11" WC, then turn the tank off and bleed the system down to 8" WC and see if it will hold there.  I have seen some that you cant bleed down to 8 due to a bad shutoff valve.
Steve

1997 U270 36' build 5179
Motorcade #18147