Re: generator power surging, but engine running fine
Reply #7 –
Last spring mine was doing the same, run normal for about 3 to 5 and then voltage jumped up to 160 or 170 on both legs, Progressive EMS would throw it off line. Isuzu engne always sounded normal. I would follow Brett's advice and then call Jeff. Voltage regulator is specific to brushless or brush generator, and according to model. Mine a late 1997 Protech 8Kw. Voltage regulator solved the problem. 625 hours at time of problem. Have put another 100 hours with clean, stable voltage. Did have to tighten the fan belt because it shut down from high temp, as it was supposed to.