Re: SOLAR / BATTERY - UPDATE - pictures
Reply #8 –
All cabling needs to be the same length AFAIK. The inner batteries on the string should have curled up cables. Then to a common bus bar or whatever. Otherwise the end batteries are doing the work more, regular battery rotation and testing would be needed more often if the cabling varies. Marine tinned cabling is preferred. I have seen bigger size same gauge wiring around, American wire gage? 15/16Th? stuff
You have done the rest top notch. Really like the Lifelines as they charge 20% faster and require lower voltage during all phases and can be equalized if any reduction in capacity is measured.
Most batteries require either 1/5th capacity or 1/20. Too low of a charging rate does not desulfate the plates correctly as far as what lifeline says.
Probably why Foretravel sized their alternators to be 1/5 C compared to the battery bank capacity. New IH-45's coaches with 6 8g8d's have a 345 amp alternator.
You may need much more alternator to charge your bank correctly.
Everything is in the details at this point.
Good thing with the Lifelines is if a capacity reduction from short cycling is noted they can be restored. Non lifeline agm's cannot be equalized..
You might need to restore a partial string to get enough amps to do it at some future time,,
My understanding is that after 15-20 cycles the batteries have reached their full capacity. Maybe measure them then?
My thoughts were if I had that large a capacity system that 2 alternators might be needed. In your case equalization is available instead.
Gels or Lifelines are the top of the line.
The Victron did not show a reduced voltage AGM setting so a flooded cell profile might be more correct. .2 volts less than normal agm's
See the lifeline tech sheet to double check my info I read.