Re: Puzzling aquahot control issue, second chapter, the double nut.
Reply #8 –
That double nut is used fairly commonly by other manufacturers. I had similar issues with my Newells.
Checking for voltage and finding 12+vdc can mislead you to pass over a problem like this. Voltage will pass until you start pulling amps then the voltage can drop below what is needed. Not easy to find these problems but can be caused by loose connections like this, bad wire crimps (been there multiple times), wires corroded inside the insulation (been there too), etc.
For future troubleshooting you can try watching the voltage across a connection like this and see if it drops. If it does drop more than expected there is a problem somewhere between.
Good find! You'll be an expert in no time.