Topic: AH furnace problem (Read 382 times) previous topic - next topic

AH furnace problem

Had AH serviced today to include new #2 circulating pump, fuel pump and gear, blower motor with clutch.  Every thing seemed to be running properly all zones, checked by AH service guy.  Got home; now #1 system not answering thermostat, fans for the exchangers not running.
Any suggestions?
Thanks, Mike

 
Mike Brady
'97 U320 SE. #5137
'13 Honda Fit
Willow Springs, MO

Re: AH furnace problem

Reply #1
Go down in the basement and check to see if one of the cube relays has come loose.

Mike
Pamela & Mike 97 U 320

"It's not what happens to you, but how you react to it that matters."

Re: AH furnace problem

Reply #2
Bingo!  Just back from checking that and found it just loose enough,  and was going to delete the  post. 
Thanks, Mike
Mike Brady
'97 U320 SE. #5137
'13 Honda Fit
Willow Springs, MO

Re: AH furnace problem

Reply #3
They make a retaining clip for those but I don't recall the part number that fits our style base and relay.

Mike
Pamela & Mike 97 U 320

"It's not what happens to you, but how you react to it that matters."

 

Re: AH furnace problem

Reply #4
I bought retaining clips. I could not get them to stay on.  >:(
Tim Dianics
Pam Sapienza
Vader PupZilla Labrador Canine Beast (AKA Pup)
Columbia, MO
1996 U320 4000
2021 Jeep Gladiator, Diesel