Nice idea but it may not operate as intended. Air conditioning is all about heat transfer and the condenser does that getting rid of the heat. The current location of the condenser will make that impossible. It must be located in free air and according to all manufacturers minimum clearances which for mini split condensers (that I am familiar with) would be 5" to a wall and 20" to anything above. Having the condenser in the storage will not meet those requirements. This will make it difficult to achieve a temperature drop as desired, it will run continuously trying to dissipate the heat when the storage area becomes hot which will only take a few minutes.
You would need a ducted intake and exhaust system, or possibly some sort of flex piping allowing the condenser to stand outside when you are stationary.
I may be wrong, I am basing my comments on Mitsubishi and Bryant units that I see regularly, I could not find the installation manual for yours on line.