PowerTech 8KW generator runs 45 minutes and stops

Been chasing an intermittent failure of my 1997 IDL 8000FT 3 cylinder Izuzu 3LB1PV-02 1.12 L diesel generator. When it stops the overspeed/no speed error shows up on the ES52 control box as a steady (not flashing) error every time. This indicates overspeed, however, the generator is running and sounding normal when it dies, operating under a load with steady voltage and 60 to 61 HZ. It sounds like it has simply been turned off. It will generally run for 20 or 45 minutes before shutting down. Temperature as indicated with IR thermometer shows normal temperature, about 165 F at thermostat housing. I have had it shut down from high temperature due to a loose fan belt, bad radiator, and inadequate airflow around fan shroud. Then the error was "high temperature." All those issues have been corrected for several years. A fellow Foretravel owner walked by while I was testing my generator and said, "It sounds perfect." Then it just died.

I removed the PreHeat relay and swapped it with the Shut Down relay in the control box. No difference. I have disconnected and cleaned the fuel shut off solenoid and run resistance checks on both the start and hold in coils. The higher amperage start coil measured 2 ohms resistance, while the hold in side measured 36 ohms resistance. Searched around and found the resistance on a John Deer tractor solenoid is 2 ohms and 12 ohms, so my hold in resistance is 3x what a John Deer tractor specs out as normal. All my research indicates that the start side of the solenoid has low resistance, and the hold in side has higher resistance. Haven't found data on the proper range for the 3LB1 solenoid.

My best theory at this moment is that the hold in circuit of the fuel shut down solenoid is out of spec, and after it has been on for 20 to 45 minutes, it stops holding in and shuts the engine down. I did have one instance where the engine started and then immediately died on three separate sequential start sequences. That's a pretty classic case of a hold in malfunction on the fuel shut off solenoid.  Of course the next day it started right up and ran for 45 minutes. It does seem to run much shorter if I try to run right after an ES52 indicated shut down with overspeed error.

If the fuel shut off solenoid hold in circuit breaks down, would the falling RPM from fuel shut off trigger an "overspeed" error in the ES52? I.E., RPM is out of range of normal operation while it falls to zero.

At the moment we are at the SKP COOP Ranch in Lakewood, NM where we recently purchased a lot. I would like to get this resolved before Quartzsite in January. I read Frank's generator saga while camped with Al at Gone Fishing Resort. It was a bad connection at the shutoff solenoid, which is why I removed my connector, cleaned it with Deoxit D5 and reconnected. The contacts looked like they would benefit from some cleaning.

The "work perfectly and then not" scenarios can be frustrating to diagnose. If 36 ohms is out of spec for the solenoid, then a new solenoid looks like the next step. One other possibility is that the AC to DC transformer that feeds the no speed and overspeed inputs on the ES52 could be going bad. Any help would be appreciated.
1998 36 foot U270 Build No. 5328 WTFE, 900 watts solar, Victron controller, B2B, bat monitor, 600 AMPH lithium with 2018 Chevy Colorado toad, SKP #110239, Motorcade #17781, 2021 Escape 17B for when Coach is broken down and campsites are too small, retired and full-timer since Dec. 2020. Part of RV family since 1963.

Re: PowerTech 8KW generator runs 45 minutes and stops

Reply #1
Let the engine run until it shuts-down.
Find a way to hold the shut-down solenoid in the run position.
Hold the solenoid in the run position.
Restart the engine, let it run for 1 hour+. If it shuts-down the solenoid is not the problem.
 
Tim

My 2 cents
Tim Dianics
Pam Sapienza
Vader PupZilla Labrador Canine Beast (AKA Pup)
Columbia, MO
1996 U320 4000
2021 Jeep Gladiator, Diesel

Re: PowerTech 8KW generator runs 45 minutes and stops

Reply #2
His number should be on the forum,call Jeff at Powertech would be my first choice.
96 U270 BUILD 4810
85 380SL
Drummonds TN.

Re: PowerTech 8KW generator runs 45 minutes and stops

Reply #3
I had the similar occurring last year. A long time friend and mechanic told me to remove the fuel cap and give it a go. He was Going after the tank venting improperly as the problem. I had many reasons  to discount his thought... but that was it! Two new caps,done.
At least its an easy test,
anouther two cents,
2002 U320 36'

 

Re: PowerTech 8KW generator runs 45 minutes and stops

Reply #4
Sounds like you did extensive testing a lot more than I would have known to do. When my generator ran for a while and then shut down it was always due to airlock in the cooling system with the remote radiator. It took a while for me to get that completely bled. But then I had an overtemp alarm on the remote panel that has the idiot lights on it.
Don't know why Foretravel did not have a control panel and readout inside the coach for that very expensive piece of kit. Would have been nice to know things like temperature, voltage, hertz... Although my picture on color control can tell me some of that.
Hope you get it worked out.