Topic: Aquahot ignites out of housing but not jn (Read 400 times) previous topic - next topic

Aquahot ignites out of housing but not jn

I'm having some issues with the aquahot hot in the 04. I replaced the coil because that was bad. Put a new nozzle on and have tested the flame sensor.  I can get the unit to ignite and burn with it not in the housing. Just pointing out of the bay and it works fine. But it doesn't ignite when it's installed into the aquahot tank. I got it to light with it sitting close to the installed position and bolted it in place and it ran fine. I need to let it cool down and see if it reignites. I tried it after it sat for a while with all the heaters running. But it didn't start. It might have been too hot. Is there anything to look for that would cause this?
1991 U300 Side Aisle 6V92 Silver #3897
2004 U320 40' #6246

Re: Aquahot ignites out of housing but not jn

Reply #1
Wait for Rudy for conformation but flame sensor is suspect. How did you test it? Also your lighting the burner in the bay out of the chamber could be catastrophic.
1999 40 ft. U-320 wtfe build 5563 Chuck & Lynda's "Rollin' Inn"  2030 watts solar
prev. mh's 71 GMC 5 yrs. 73 Pace Setter 1 yr. 78 Vogue 5 yrs 81 FTX 40ft all electric 18 yrs. 1996 Monaco Signature 3 yrs.
2014 Grand Cherokee Overland
Dream as if you will live forever. Live as if you will die today.  James Dean

Re: Aquahot ignites out of housing but not jn

Reply #2
My bet is the ignitor points are firing into the swiller when mounted to heater.

Remove burner, very carefully adjust ignitor points to just touch the "V"s in the gauge.

You can put the combustion chamber onto the burner when it is dismounted to watch the points arch.  If into swiller, everything is working but no fire is ignited
Rudy Legett
2003 U320 4010 ISM 450 hp
2001 U320 4220 ISM 450 hp
1995 U320 M11 400 hp
1990 Granvilla 300 hp 3208T
Aqua Hot Service Houston and Southeast Texas

Re: Aquahot ignites out of housing but not jn

Reply #3
I think I may have found the issue. I had the electrode spacing tool on the flats of the nozzle, not down on the lower nut. I think the electrodes are out too far.

Also, according to this chart for the 1553 controller, it's supposed to run the fan for 10-25s before igniting, and then light off? Does this sound right? Mine is lighting the instant it powers up.
1991 U300 Side Aisle 6V92 Silver #3897
2004 U320 40' #6246

Re: Aquahot ignites out of housing but not jn

Reply #4
Firing immediately is a failure of the control unit.  Congratulations on fixing the ignitor gap but you need a new control unit now
Rudy Legett
2003 U320 4010 ISM 450 hp
2001 U320 4220 ISM 450 hp
1995 U320 M11 400 hp
1990 Granvilla 300 hp 3208T
Aqua Hot Service Houston and Southeast Texas

Re: Aquahot ignites out of housing but not jn

Reply #5
Thanks for the insight Rudy and confirmation that the controller is bad. Looks like I'll be in touch with Frerichs to get a rebuilt unit. The Spheros black box units seem to get mixed reviews.
1991 U300 Side Aisle 6V92 Silver #3897
2004 U320 40' #6246

Re: Aquahot ignites out of housing but not jn

Reply #6
Do not purchase a Sperios black box.  A reman silver box is fine and a new one is even better but lots more money
Rudy Legett
2003 U320 4010 ISM 450 hp
2001 U320 4220 ISM 450 hp
1995 U320 M11 400 hp
1990 Granvilla 300 hp 3208T
Aqua Hot Service Houston and Southeast Texas

Re: Aquahot ignites out of housing but not jn

Reply #7
Aquahot test fire
1991 U300 Side Aisle 6V92 Silver #3897
2004 U320 40' #6246

Re: Aquahot ignites out of housing but not jn

Reply #8
Replaced the controller and readjusted the ignitors and everything seems fine. It ran the blower for a bit and then ignited without any issue. Looks like the Aquahot is working perfectly. Now it just change the fluid it in and it should be good as new.
1991 U300 Side Aisle 6V92 Silver #3897
2004 U320 40' #6246

 

Re: Aquahot ignites out of housing but not jn

Reply #9
Thanks for the followup. 