Re: Generator not starting/stopping from dash switch
Reply #7 –
White,
1. On your age coach '98 the generator starts off the house batteries UNLESS a previous owner has changed it.
2. If your inverter is only putting out 94vac either the house batteries are low/dead, bad inverter, or possible bad connection in transfer switch.
3. The clicking may just be the fuel pump running.
3 a. You should be able to here it (fuel pump) run also if you start the gen. from the start button on the gen. control panel also.
4. When you start the generator from the gen. control panel will it run for an extended amount of time like at least till your transfer switch swaps over?
5. Did you check your AC voltage while on gen.?
6. By the way you talk in first post this has been going on a while. Is this correct?
7. What gauges are you talking about being replaced?
7a. How long ago?
8. It could be like Kieth has mentioned someone left a wire off the or miss wired the dash start switch.
9. Is your dash switch a momentary switch or is it an on/off switch? That age/time frame it could be either. This info will help with which start control system you have. Not all have the same style latching relay system.
10. We started with the simple stuff now it gets more complex but with the knowledge here it can be fixed.
Mike