Power Tech Issue


  Gen started right up after 5 months in garage, runs fine but will not generate. Reset all breakers, fault lite will not go off. 1200 hrs Pancake gen. Any thoughts? Made appt in Leesburg Fl. Powertech has a service center. Hope its not something I missed. Thanks John
John & Judy
2006 Phenix 40'

Re: powertech gen

Reply #1
Did you also reset the on-generator breakers?

Might also check for power IN to the ATS from the generator as a failed ATS can give no power symptoms to the coach.
Brett Wolfe
EX: 1993 U240
Moderator, ForeForum 2001-
Moderator Diesel RV Club 2002-
Moderator, FMCA Forum 2009-2020
Chairman FMCA Technical Advisory Committee 2011-2020

Re: powertech gen

Reply #2
I am confused how it runs with the Fault light on, must be a new design.  Does the fan n gen radiator run?

Re: powertech gen

Reply #3
   Took coach to powertech in Leesburg Fl, new brushes & clean armature. Works great except fault light won't go off. Any suggestions? Everything else checks out fine. Thanks John
John & Judy
2006 Phenix 40'

Re: powertech gen

Reply #4
unscrew the bulb or hit it with a hammer. That should put it out!!! What do you say Dave?
John
Coachless, now use aircraft. 2003 Ford Travelair TC280 class C. Super shape. Just for 1 yr .
1994 Ford E350 ClassC,total renovation inside and out. Now sold.
2000 U295  36' Cummins 350 c/w Banks Stinger, Resonator upgrade,Solar, LED lites.Residential fridge with slide out pantry. Build 5674. Sold
ex 92 GV 022C ored Cummins. Sold
ex 95 GV240 cat 3116. Sold
2017 Mini cooper s & 2016 land Rover LR2 HSE  LUX.
jhaygarth@aol.com    SKP #130098
treat everyone as you would like to be.

Re: powertech gen

Reply #5
I guess I still confused, after having it to Power Tech, had it fixed almost, but wonder why they could not figure out the fault light issue,  Duh ! !
Wonder which wiring diagram it uses ?  Would hate to use a large hammer John, might make a small mess, but would put the light out.
However if my Fault light was on, I would check for:
Loss of speed signal
Low oil pressure
High engine temp
Over crank
Aux input
Can it be reset from engine control panel?
Do any of the panel indicators light or blink ?
Close it up and have a beer.


Re: powertech gen

Reply #6
Another little item, the coolant level switch if low, will light the fault light and depending on how it is set, it could let engine keep running OR could be set to stop engine. Terminal 16 on the auto-start panel ES-52 in my manual, 01, 320.
Worth a snoop  ^.^d

Power Tech Issue

Reply #7
Have to admitt that I got mislead by my little generator, when starting cold, it started, runs rough, would clear up on about 20 seconds, SO I figured it must be the flow plugs either not getting the 12VDC or one or more glow plugs had gotten burned out.  Boy was I wrong, after spending much  time checking all the above and all is in fine shape, I realized I have a bad section of fuel line and it is either leaving air into the system on the return side or have a bad section on the suction hose.  Either way I will get it, just had to mention this little issue, as might help others.  ^.^d

Re: Power Tech Issue

Reply #8
Dave I have the same problem, However I just changed the engine controller and did not set the DIP switches to turn on the glow plugs long enough. Got to take it back apart and reset. I guess I'll wait until it's about 20 degrees and the gen won't start then I fix it, more fun like that.
Bruce, Linda, and Macy
Zoey RIP 1/20/19
1999 U295 40' build #5400
2017 silver Jeep Wrangler, 1260 watts of solar on top
Moving around the country

Re: Power Tech Issue

Reply #9
Bruce, I sure recommend setting the glow plug timer now and save your starter motor, I know it is a beast to get into the controller, but while the weather is nice is a perfect time to do it, not when it is raining, 32f and 45 mph wind and you gotta have the generator right NOW.
Give it a thought  ;D

Re: Power Tech Issue

Reply #10
With the temps in the teens at 8000', 30 seconds of glow starts the Kubota generator within ten seconds of cranking. Dave, do the glow plugs shut off on the later generators after a short time? Does the glow timer have a temperature sensor? A lot of diesels keep the glow plugs on for an additional 45 seconds or so after the engine has started to reduce air pollution.
Pierce and Gaylie Stewart
'93 U300/36 WTBI
Detroit 6V-92TA Jake
1140 watts on the roof
SBFD (ret)

 

Re: Power Tech Issue

Reply #11
Pierce, The Glow Plug timer is adjustable some what, but no to temp sensing, it is not an intelligent type.  Standard Dyna Gen ES52-12-A-LS module, have three on my desk here right now, will install two  today,converting two old units from old style controls to upgrade to the Dyna Gen, Have done many of these little babies.