Re: Coach Fire Supression
Reply #3 –
Since I was asked, I don't know how effective an ounce or two is going to be, I assume that you do ? This system uses 1 lb of "clean media", Novec, slightly more effective than Halon, but has no impact on the environment. The SS30 extinguisher which many of us have for our refer compartment contains a like amount of Halon. The SS30 activates when the temp at ITS location reaches activation temp, it then floods the compartment. This unit melts at the location of the FIRE then it empties its content where it's needed....on the fire.
The 40B rating becomes fairly irrelevant when protecting enclosures with clean agents. The "40" is based on coverage for an open area, in square feet. In the case of the 40B:C that would be a 40 sq ft fire. Clean agents are pretty ineffective in the open. I would hate to face a 40 sq ft B fire with a 20 lb halon extinguisher, or 100 lb for that matter. For enclosures protected by clean agent systems, normally a % of saturation for the cubic feet protected is used to determine the amount of media required.