Re: Propane Generator - It starts and runs as long as you hold down the start button
Reply #39 –
Another cause of hard starting/poor running on Liquid LP generators is that the very good quality on-generator regulator is laid on its side instead of being installed vertically. That causes the longer chain hydrocarbon contaminants in the propane to accumulate in the regulator and eventually clog it up. The regulators can be replaced or rebuilt. If rebuilt, make sure to specify the HIGH TEMP/SILICONE gasket kit needed because of the regulator's location in the generator.
Note, I am not suggesting this is the cause of the OP's issue, he could easily have an electrical/control board issue.