Re: Two Generator Questions
Reply #1 –
Richard,
In regard to question 1
Have you had a chance to plug in to a 50 amp power pedestal after this occurred?
If so did you have power back on both legs?
If you are comfortable working around electricity you need to check the contacts in you transfer switch to see if you have power coming at least to there from the generator while it is running. You could have burnt up a contactor in your transfer switch and nothing is wrong with the generator itself.
Question 2
While all this was going on did the radiator cooling fan trip/ quit running when you lost power? If so you may have just boiled the antifreeze due to no cooling fan. If this happened then your power problems may be in the generator end rather than the transfer switch end.
Your generator also has a water pump belt. That belt needs to be checked as it may have broken causing the engine to overheat.
Did the generator shut down on overheat or did you kill it at the switch before it shut it's self down?
On our Isuzu it has 3 places to bleed air out of the system if you don't have antifreeze at all the air bleed pet cocks it will get hot also.
This is just several things to look at to help narrow down your problem.
Pamela & Mike