The two phases are supplied by a center tapped transformer. The utility provides three phase power from the generating station, hence the main supply poles carry three wires. Thus there are three phases at 120 deg. That is not the case with what is supplied as 50 amp power in RV parks. Only one phase is tapped at the pole and the center tapped transformer is what gives 2 phases at 180 deg.
There should never be more than 50 amps present on the neutral as 180 deg opposite phase is subtractive IE: leg 1 running at 20 amps Leg 2 running at 15 amps will show 5 amps on the neutral. Wire both legs to the same phase and it is additive and you will have 45 amps.
Keith