Topic: Why On Off on Breaker at Genset? (Read 428 times) previous topic - next topic

Why On Off on Breaker at Genset?

Genny has these switches.  Why not just a reset?
Randy (N4TDT) and Karen Crete
Sarasota, Florida
SOLD:  2000 U270 34' WTFE Build 5756 "Ole Red"

Re: Why On Off on Breaker at Genset?

Reply #1
Those aren't just switches they are breakers. If they trip you will have to reset them. They should be your line breakers.  The little round fuse holder should be for your field it should have like a 2 to 3 amp fuse in it.

Pamela & Mike
Pamela & Mike 97 U 320

"It's not what happens to you, but how you react to it that matters."

Re: Why On Off on Breaker at Genset?

Reply #2
Genny has these switches.  Why not just a reset?
The generator is used for other applications also. Not just RV use. Someone using it in a field application might plug directly into it.
91 GV U300 Unihome 40' Build 3811
6V92TA Detroit

Re: Why On Off on Breaker at Genset?

Reply #3
Conductors need to be protected from overload and short circuit conditions at their source.
Justin & Cathy Byrd
1995 U280 "Old Faithful"
36' Build #4673
C8.3 Cummins
Allison MD3060R 6 speed - retarder
Powertech 10KW  4cyl Kubota

 

Re: Why On Off on Breaker at Genset?

Reply #4
I recently had problems with a troublesome 10a circuit breaker.  After replacing it without solving the problem, I investigated more thoroughly.  I found three wires in the control box where vibrations over time had rubbed through insulation creating the potential short circuits.  They would have been excellent smoke generators if the the CB was resetting.