Re: New owner of a u280 ORED (onan genset question)
Reply #1 –
blaine,
Welcome to the ForeForum.
Generator WILL start with shore power connected. The ATS (Automatic Transfer Switch will only allow one source of 120 VAC to the main breaker box.
Start your troubleshooting at the generator itself. Check voltage between the large positive lug and any clean piece of metal on the generator (the ground). What is reading before and while you push the "start" button on the generator?
Does it try to turn over?
Turn over but not try to run?
Tell us exactly how far into the "run process" it gets.