Re: inverter circuit breaker panel question
Reply #29 –
Craneman, most likely the way your rv is wired, you are only using one half of the capability of the SW3012, so you do not really have 3000 watts available, however you do have a great unit with 150 watt charger with many changeable settings thru the remote.
To see if you are using the entire 3000 watt capability you would have to look at the AC input and output connectors on the SW3012. I would expect for you to see only one of the two line inputs and only one of the two outputs being used.
Those interested may check out the attached manual for the SW3012 and the installation guide for the SW units from Xantrex. In order to get 3000 watts from the SW3012 you need to use both line inputs of 120 V line inputs from the 50 amp service coming in. See the attachment for the manual, the section on wiring the AC input and output of the SW3012.
I have owned two SW3012 in previous rvs, and found them excellent, however because of the rv wiring in the two Monaco Signatures, I used only one line of the two line inputs from the 50 amps coming in.
When I bought my current FT I chose the SW2012 as I knew I would only need it's 30 amp AC input and output for the FT wiring.
To be fair in comparing the two, the SW3012 has a 150 amp charger, the SW2012 a 100 amp charger. Given the choice again I would choose the SW3012 for the larger charger over my current SW2012. I also attached remote instructions to get an idea of how flexible your SW3012 is thru the remote control.
If ever having trouble with the SW3012 after changing settings you can load the defaults by doing so thru the remote. At one time I had created an issue after changing the low inverter cutout from 10.5 to 11.8. I had to change back to the 10.5 default. My issue was when I ran the toaster along with the microwave, the inverter would shut down as it saw less than 11.8V. At the default 10.5 all is fine.