no Basement heat '02 230.

Had the Aquahot serviced and  replaced several pumps..  Heat all zones except it seems to not have any heat in basement [heat exchanger in water manifold bay] hoses are cool to the touch,
I have turned the water manifold bay snap disc up to 40 degs.. currently 30 degs outside and dropping..
Is there a shutoff in the AH bay or might it be something else??
Down to 20 degs tonight
ANY Ideas???
'02 40' U320t  4010WTFS Build 6036 1 slide
Motorcade # 17841
SKP 151920
Retired truck driver
 5 million miler
Still have itchy feet for travel

'02 U320 Re: No hot air from Bathroom and Bay heating elements

Reply #1
Grrrrr...Just had pumps replaced and AH serviced.. have heat in LR,Bedroom, and bath registers.. but no heat [hoses cool to touch] in wet bay. did up the anti with the snap thermostat set to 40ish..
currently 30 deg on the way down to teens tonight.
'02 40' U320t  4010WTFS Build 6036 1 slide
Motorcade # 17841
SKP 151920
Retired truck driver
 5 million miler
Still have itchy feet for travel

Re: '02 U320 Re: No hot air from Bathroom and Bay heating elements

Reply #2
add a small heater from Walmart in bay - the smallest space heater they make-

they usually have something like this 250 watt job in stock

Soleil Electric Personal Ceramic Mini Heater 250W Indoor Wood MH-08S -...

they sometimes have a 1500W heater in stock with a thermostat

or Tractor Supply or other farm store usually has a plug that goes in the 110V outlet that has a 40 degree or 34 degree thermostat to turn off and on a small heater

hope it all works out - even the old incandescent bulb in a pinch trick will help
Tim Fiedler    2025 LTV Unity MBL on Order
2000 Chevy Tracker 2 Door Convertible 4WD Now lifted 4.5"
1985 Citroen 2CV6 Charleston
Murphy Rebel on wheels with 175HP Titan
Cessna P337
1980 48' Westport MY (!/4 Share)

Re: no Basement heat '02 230.

Reply #3
Could be:
That zone is air locked if it didn't get purged completely after the replacement of the zone pump.
The check valve at the zone pump is stuck closed. A gentle tap with a hammer may pop the flapper loose.
If your unit has 3 relays (depends on which unit you have) that control the zone pumps the center one may be loose.
Do you have heat in the bathroom when that thermostat is on?
Are the fans in the basement radiators running when you turn down the basement thermostat?

Mike
Pamela & Mike 97 U 320

"It's not what happens to you, but how you react to it that matters."

Re: '02 U320 Re: No hot air from Bathroom and Bay heating elements

Reply #4
Grrrrr...Just had pumps replaced and AH serviced.. have heat in LR,Bedroom, and bath registers.. but no heat [hoses cool to touch] in wet bay. did up the anti with the snap thermostat set to 40ish..

Have you tried tapping the zone valve for the BA/bay?  Sometimes they stick closed.  (this was actually the first issue we ever had with our '03, way back in '04.  Triana advised (as some members call it) "percussive encouragement" on the zone valve, and it solved the problem.
Learn every day, but especially from the experiences of others. It's cheaper!  - John C. Bogle

2000 U320 36' non-slide / WildEBeest Rescue
2003 U320

 

Re: no Basement heat '02 230.

Reply #5
Update!!
Found the issue.. the wires connected to the snap thermostat in water manifold bay were gummed up.. all good now.. thnx to everyone..especially MR Rudy!