Re: Freedom 25 converter/inverter/charger questions
Reply #6 –
And, since from ATS onward through main 120 VAC breaker panel and on to inverter, the wiring is exactly the same the same, either ATS is not seeing both legs (L1 and L2) or there is an issue in the ATS itself.
I would open the ATS and check for power IN and OUT after verifying that indeed your CG outlet is good.
To check CG outlet:
Either outer straight to center straight or center round= 120 VAC
Center straight to center round= 0 VAC
Outer straight to outer straight= 240 VAC though a reading of 0 with other readings being correct will work.