Re: Hughes Power Watchdog EMS indicating no neutral
Reply #1 –
First be careful. Electrical shock can kill. If you do not have a clue what you are doing, leave this up to someone that does.
Locate the breaker box., which I think is under the front of the bed. Remove cover. You should be able to see Some big #6 or so wires coming into the panel. You should also see some bars located to the side, or bottom that have white wires attached. That is the neutral bar. There will also be a bar where either green or bar copper wires are attached. That is the ground bar. Now take a voltage tester and verify it works by taking the terminals and plugin into an outlet in your home that you know it works. Sometime you have go and verify you have the meter on the correct setting. If you are getting 120 or somewhere close to to that then you are ready to test the panel.
With generator running and seeing that you have power in coach such as AC fan running You are going to test between the big black and big red wires. If on generator you probably will get a zero or so reading. This is because your generator only puts out 120V. If on shore power and connected to 50 amp 120/240v outlet you should get 240 volts or somewhere close to that.
Test between the big black and the neutral bar You should get 120 volts
Test between the big Red and the neutral bar You should get 120 volts
Test between the big black and the ground bar You should get 120 volts
Test between the big Red and the ground bar You should get 120 volts
Test between the neutral and the ground bar You should get 0 volts
If all of your tests show what I have above then everything is correct