Re: 1986 Grandvilla electrical issues
Reply #1 –
Mike,
If you are safe working around 120/240 VAC, with power off, remove the lid to the ATS. Torque all screws holding wires and verify no burned wires.
By checking power in the ATS, both on the IN side and OUT side you will be able to determine if the issue is in the ATS or between it and the CG outlet.
Plug in and turn on CG breaker.
Normal colors are:
Hots are black and red.
Neutral is white
Ground is green
Check:
Black to white= 120 VAC
Red to white= 120 VAC
Black to red= 240 VAC
Black to green= 120 VAC
Red to green= 120 VAC