Re: Connecting powertech generator to victron cerbo gx
Reply #24 –
Tom,
I'm trying to understand how this works. I get that the generator can be started by The Cerbo GX. When you start the generator manually, it closes the NO relay on the Cerbo sending power to the closed Autogen on-off switch (in is closed and, in turn, supplies power to the generator on-off switch starting the generator. But, with the BCM-12 the generator is started by sending a pulse to a latching relay, whereas the Cerbo will be sending constant power until stopped (moving the Cerbo relay from closed to its NO position.) This is where I'm confused. Since the gen is using a latching relay for the on-off switch, I would assume its expecting another momentary pulse to turn the gen off. In the case of the Cerbo, isn't it just cutting power to the switch versus sending a pulse to trigger the gen to turn off? Or, is turning off power to the Auto-Gen On/Off switch cutting power to the generator altogether and causing it to shut down?
After removing power from the BCM-12 entirely, we were unable to get the gen to start or stop at all. With the BCM-12 under power, we could get the gen to start, but were unable to get it to shut down. Are you able to manually both start and stop the gen from the Cerbo with the BCCM unplugged from 12V power or just when its still plugged in but disconnected from the Auto-gen on-off switch?