Re: 50 amp question
Reply #1 –
Answers in SOLID LETTER CAPS
I've attached pictures of the electrical panels in our U270. I had always understood that 50 amp service gave you 50 A on each leg or 100 A total. I'm confused by the fact that what I have always understood was the main panel has 2-50 amp breakers. Somewhere along the way, I had gotten the impression that the even numbered breakers were on one leg, and the odd numbered breakers were on the other. If this is true, and both air conditioners are on the same leg. YOU ARE CORRECT, TWO 50 AMP BREAKERS FOR TOTAL OF 100 AMPS @ 120 VAC. AND, YES, LOADS ARE STAGGERED BETWEEN THE HOTS AS YOU GO DOWN THE BREAKERS.
But, the second Panel also has a 50 amp breaker, but the only large draw appears to be the microwave. THE SECOND PANEL WILL BE FROM THE INVERTER "OUT" AS ONE INPUT AND MAIN BREAKER PANEL AS PRIMARY INPUT.
2. When I connect to 30 amp with an adapter are all these circuits in both panels "hot"? And, if so can I manage running all of them, in different combinations so long as their combine draw is 30 amps or less? CORRECT. INSIDE THE 30 AMP MALE TO 50 AMP FEMALE ADAPTER, THE SINGLE HOT ON THE 30 AMP END IS WIRED TO BOTH HOTS ON THE 50 AMP END. TOTAL OF 30 AMPS @ 120 VAC AVAILABLE.
Thanks
2. Why is there a second panel. SEE ABOVE-- ONLY SUPPLIES THOSE CIRCUITS THAT CAN BE RUN BY THE INVERTER.