Re: I thought the inverter was dead. Nope!
Reply #3 –
Do any of your wall outlets work when you are on shore power, or when the generator is running?
You can't have two different active AC electric sources simultaneously powering your main AC panel. For instance, you can't connect the (running) generator and shore power to the main panel at the same time. That's why you have the shore power/generator ATS. It allows one or the other to actively power the main panel, but not both at the same time.
You also can't have the (active) inverter connected to the main panel at the same time as the shore power or the (running) generator.
If you don't have a inverter transfer switch (or relay) then you must have two separate AC power circuits - one for the shore power or generator, and one for the inverter. In that case, you might also have two separate AC circuit breaker panels - main panel and inverter panel. The inverter powered panel would feed one or more dedicated inverter outlets that are only "hot" when the inverter is running. If you have this setup, check the inverter panel for tripped circuit breakers.
Lift the bed mattress platform and look in the enclosed space at the foot of the bed. Any AC electrical stuff there?