Re: Looking for the reason - Charger breaker tripped?
Reply #26 –
Scott,
Part of the answer will depend on actual location of the components. If that 6-2 wire from main breaker box to second ATS could be used to provide power IN to the inverter/charger, likely using a 30 amp breaker, then the inverter/charger's internal ATS could be used and remove the secondary ATS. The sub-panel could be wired from the inverter/charger 120 VAC output.
Bottom line, unless you will be running enough different appliances to exceed the inverter's capacity, I see no reason for a secondary ATS. If you might exceed the inverter's capacity, I would run heavier wire from main breaker box to inverter IN and use a 30 amp breaker. Then inverter OUT to ATS. But, make sure that the "favored" position for the secondary ATS is shore power!
Brett