Re: Battery usage percentages
Reply #104 –
Just note that you can only safely parallel connect banks of solar panels if each bank produces exactly the same voltage, otherwise you will be applying the voltage differential across a length of wire, heating the wire, possibly to destruction, and wasting power.
I would feel safest if each parallel connected bank is the same configuration and the same solar cell type, otherwise there might be small differences in voltages under identical conditions. I wouldn't try paralleling an amorphous UniSolar cell with a traditional crystalline cell, or two cells from different manufacturers with different blocking diodes used or not used.
Series connections on the other hand are just fine, as long as you never under any conditions (for example no load and cold) exceed the controllers max PV voltage.