Re: Damaged battery cable
Reply #7 –
We are looking at two things here. 1. Repair of the insulation. Several solutions are given above. I like the self amalgamating tape or the shrink tube solution IF it is the adhesive core kind. If the copper conductor is damage see below.
The non splice method only applies IF the copper conductor is intact. If not the current carrying capacity of the conductor is reduced and if a load close to the conductors upper limit is applied the cable will heat up where it is thinnest.
Make sure that corrosion has not got into the cable as it will wick along the strands and give you a problem on the future.
Keith