Topic: Overloaded circuit (Read 910 times) previous topic - next topic

Overloaded circuit

Yesterday morning the heaters I had on blew the breaker. I moved one of the heaters and started them up. Beaker blew again, so
I checked and found 8 receptacles on one circuit, that's nuts. Now I have to find a way to fish new wires so I can make more
circuits. It's the bathroom front area and the basement all on one circuit. Has anyone fixed this.   
Peter and Frieda Morin
1999 36ft. U320 Foretravel
Build # 5436
1998 Suzuki Sidekick Sport

Re: Overloaded circuit

Reply #1
Try using on of the outlets on the drivers side. They are in a different circuit.
Bruce, Linda, and Macy
Zoey RIP 1/20/19
1999 U295 40' build #5400
2017 silver Jeep Wrangler, 1260 watts of solar on top
Moving around the country

Re: Overloaded circuit

Reply #2
How many heaters are you running?  How many amps total draw if they are all "on" at the same time?  What else is running at the same time time as the heaters?

I run 6 of the small 1500W (12.5 amp) LASKO ceramic space heaters (PLUS our residential fridge) in our coach without popping any breakers.  Every winter I keep 4 heaters in the passenger area, and two in the wet bay.  There must be times when all of them are running simultaneously.

Note:  I DO leave the heaters set on "LOW" heat setting.  Not sure what the amp draw is on that setting.  8 amps?

Possibly a weak circuit breaker?
1993 U280 SE 40' WTBI, Build: 4359
C8.3 300hp, 6-Speed, Exhaust Brake
960 watts on the roof (6 x 160)
Sorento (or BOLT) on a Kar Kaddy SS
"Nature abhors a vacuum"

Re: Overloaded circuit

Reply #3
Don't forget some (many) of the outlets are run through the inverter, so take into account inverter limitations.

If you do modify wiring from OEM, be sure to document it well for when you sell the coach.
Learn every day, but especially from the experiences of others. It's cheaper!  - John C. Bogle

2000 U320 36' non-slide / WildEBeest Rescue
2003 U320

Re: Overloaded circuit

Reply #4
I found a receptacle under the couch that is on a different circuit. Both sides of my coach are on the same circuit. 8 receptacles on
one circuit is too many. I know why it blew, I just didn't think all the receptacles would be on the same circuit.
Peter and Frieda Morin
1999 36ft. U320 Foretravel
Build # 5436
1998 Suzuki Sidekick Sport

Re: Overloaded circuit

Reply #5
Don't forget some (many) of the outlets are run through the inverter, so take into account inverter limitations.

If you do modify wiring from OEM, be sure to document it well for when you sell the coach.
Does the factory double ATS system by-pass the inverter while on generator or hooked to the pole?
1999 40 ft. U-320 wtfe build 5563 Chuck & Lynda's "Rollin' Inn"  2030 watts solar
prev. mh's 71 GMC 5 yrs. 73 Pace Setter 1 yr. 78 Vogue 5 yrs 81 FTX 40ft all electric 18 yrs. 1996 Monaco Signature 3 yrs.
2014 Grand Cherokee Overland
Dream as if you will live forever. Live as if you will die today.  James Dean

Re: Overloaded circuit

Reply #6
I don't run heaters off the inverter in fact I usually only run the tv and charging for laptop and tablet.
Peter and Frieda Morin
1999 36ft. U320 Foretravel
Build # 5436
1998 Suzuki Sidekick Sport

Re: Overloaded circuit

Reply #7
Does the factory double ATS system by-pass the inverter while on generator or hooked to the pole?

YES, the second ATS serves as a high-amp substitute for the internal ATS found in the inverter.
Brett Wolfe
EX: 1993 U240
Moderator, ForeForum 2001-
Moderator Diesel RV Club 2002-
Moderator, FMCA Forum 2009-2020
Chairman FMCA Technical Advisory Committee 2011-2020

Re: Overloaded circuit

Reply #8
I don't run heaters off the inverter in fact I usually only run the tv and charging for laptop and tablet.

If the heater is on an outlet that can be supplied by the inverter  (look at your sub-panel if you have one) your inverter is on and no shore power or generator, it WILL run on the inverter.
Brett Wolfe
EX: 1993 U240
Moderator, ForeForum 2001-
Moderator Diesel RV Club 2002-
Moderator, FMCA Forum 2009-2020
Chairman FMCA Technical Advisory Committee 2011-2020

Re: Overloaded circuit

Reply #9
Are my 110 outlets supposed to be hot  while unplugged or genset not running?
 I only have a new small circuit that runs my fridge  through a new invertor .

Re: Overloaded circuit

Reply #10
From one old guy to another old guy, it is not the number of outlets on a circuit that count, it is what is plugged into them that matters. 
The primary function of a circuit breaker is to protect the wiring,  in other words to keep the wiring from getting hot and starting a fire. According to the electrical code, size 12 awg copper wire can only carry 20 amps and it is connected ( or should be) to a 20 amp breaker:  14 awg - 15amps; 10awg - 30 amps etc.  I agree with you that FT should have put in another breaker and circuit for some of the outlets up front on the coach.  On my coach and probably yours too, the bath and all the front outlets, basement outlets, and outlet on the side of the coach are on the same breaker.  The outlets in the bedroom are on another circuit and breaker. 
Jerry Whiteaker former owner 96 U270  36' #4831 Austin,TX-Owner Mods LCD TV w/front cabinet rebuild - LCD TV bedroom - Dual Central AC, either can cool coach w 30 amp - Skylights at roof AC openings - Drop ceiling for ducting of AC - Shower skylight white gelcoat/wood/epoxy frame - Air Springs/Shocks replaced - 2014 CRV - 8K Home Solar - Chevy Volt

Re: Overloaded circuit

Reply #11
What does ATS mean. I know I had too many heaters and a dehumidifier  plugged into one circuit and I know how to deal with it
now. If I was wiring it, it would have been at least three circuits. When I'm using heaters I turn off the inverter just in case there is
a power interruption. A heater will kill the batteries fast. The big problem is how to get a wire up the right hand side of the coach.
I can get a wire up left hand side of the coach.
Peter and Frieda Morin
1999 36ft. U320 Foretravel
Build # 5436
1998 Suzuki Sidekick Sport

Re: Overloaded circuit

Reply #12
ATS= Automatic Transfer Switch

You WILL have one for shore power OR generator to main 120 VAC breaker panel.

You will also have either a separate ATS for shore power or inverter to sub-panel for circuits that can be powered by the inverter OR it will use an ATS built into the inverter.
Brett Wolfe
EX: 1993 U240
Moderator, ForeForum 2001-
Moderator Diesel RV Club 2002-
Moderator, FMCA Forum 2009-2020
Chairman FMCA Technical Advisory Committee 2011-2020

Re: Overloaded circuit

Reply #13
Thanks Wolfe I have two transfer switches. I have a new inverter that came with the coach when I bought it and last night I opened
the manual on it and I think it will give me 120/240 volts which could be interesting as I just bought a residential fridge and then
I will put in an induction hot plate which would be nice to run on 240 volts. I have time as I won't do that till spring.
Peter and Frieda Morin
1999 36ft. U320 Foretravel
Build # 5436
1998 Suzuki Sidekick Sport

Re: Overloaded circuit

Reply #14
You will need to verify that you do have two separate HOTS and measure 240 VAC between them.

You could also have two HOTS on the same side and would measure 0 VAC between them.  Here you would have 120 VAC, not 240.

All three sources (shore power, generator and inverter) would all have to be wired for 240 VAC for you to be able to use 240 VAC appliances.  As you know, for 240, you would use two hots.  For 120  you would use only a single hot.  And, of course on either a neutral and ground.
Brett Wolfe
EX: 1993 U240
Moderator, ForeForum 2001-
Moderator Diesel RV Club 2002-
Moderator, FMCA Forum 2009-2020
Chairman FMCA Technical Advisory Committee 2011-2020

Re: Overloaded circuit

Reply #15
I was just out checking to see if the new inverter would fit without modifications and it will. The wires will have to be changed as
the ones that are there are two wire and I need 3 wire for 120/240 volt. At least changing the wires is possible. Hope fully the transfer switch is 120/240.
Peter and Frieda Morin
1999 36ft. U320 Foretravel
Build # 5436
1998 Suzuki Sidekick Sport

Re: Overloaded circuit

Reply #16
Likely the ATS will be labeled either 30 amp (single hot) or 50 amp (two hots).  But even if 50, that does not mean you have 240 VAC.  It means you COULD HAVE 240 VAC. 

ASSUMING YOU ARE SAFE WORKING AROUND 240 VAC ELECTRICITY: If 50, remove the lid and check for voltage between BLACK and RED. You will either have 0 or 240 VAC there.
Brett Wolfe
EX: 1993 U240
Moderator, ForeForum 2001-
Moderator Diesel RV Club 2002-
Moderator, FMCA Forum 2009-2020
Chairman FMCA Technical Advisory Committee 2011-2020

Re: Overloaded circuit

Reply #17
Thanks Wolfe and yes I'm comfortable around 240 volts. I used to work around 600 volts 3 phase with the electrician. I have lots of time to work this out as I won't do any of this until April
Peter and Frieda Morin
1999 36ft. U320 Foretravel
Build # 5436
1998 Suzuki Sidekick Sport

Re: Overloaded circuit

Reply #18
I check out the generator and it runs 2 legs of 120 and no 240 and the generator name plate says 120 volts so I guess I will have to change my plans.
Peter and Frieda Morin
1999 36ft. U320 Foretravel
Build # 5436
1998 Suzuki Sidekick Sport

Re: Overloaded circuit

Reply #19
A small wiring change to the generator (our Powertech 10KW) will allow two 120 legs giving 240 volts. Changing ours so it can run our well pump when PG&E cuts power next summer. Old article on the forum on how to do it.

Pierce
Pierce and Gaylie Stewart
'93 U300/36 WTBI
Detroit 6V-92TA Jake
1140 watts on the roof
SBFD (ret)

Re: Overloaded circuit

Reply #20
That's great as I wanted 240 as it is more efficient.  How would I find that old article. I find it hard to find old articles.
Peter and Frieda Morin
1999 36ft. U320 Foretravel
Build # 5436
1998 Suzuki Sidekick Sport

Re: Overloaded circuit

Reply #21
Is this what you're thinking of?

Generator Diagram to change 110vac to 240vac

Technical Help - Generator
1993 U280 SE 40' WTBI, Build: 4359
C8.3 300hp, 6-Speed, Exhaust Brake
960 watts on the roof (6 x 160)
Sorento (or BOLT) on a Kar Kaddy SS
"Nature abhors a vacuum"


Re: Overloaded circuit

Reply #23
Does this give 120/240. The 7500 Onan can be either way but not both.
Peter and Frieda Morin
1999 36ft. U320 Foretravel
Build # 5436
1998 Suzuki Sidekick Sport

 

Re: Overloaded circuit

Reply #24
Thanks for all the help it looks like it will work
Peter and Frieda Morin
1999 36ft. U320 Foretravel
Build # 5436
1998 Suzuki Sidekick Sport