Re: Overloaded circuit
Reply #10 –
From one old guy to another old guy, it is not the number of outlets on a circuit that count, it is what is plugged into them that matters.
The primary function of a circuit breaker is to protect the wiring, in other words to keep the wiring from getting hot and starting a fire. According to the electrical code, size 12 awg copper wire can only carry 20 amps and it is connected ( or should be) to a 20 amp breaker: 14 awg - 15amps; 10awg - 30 amps etc. I agree with you that FT should have put in another breaker and circuit for some of the outlets up front on the coach. On my coach and probably yours too, the bath and all the front outlets, basement outlets, and outlet on the side of the coach are on the same breaker. The outlets in the bedroom are on another circuit and breaker.