Re: Furnace not firing on 12V
Reply #1 –
Since the furnace worked with the generator running (i.e. 12 VDC house battery receiving a charge) but not on battery alone, the most likely issue is LOW BATTERY VOLTAGE.
The furnaces start sequence is:
Thermostat on
Fan starts
Fan moves enough air to close the SAIL SWITCH.
The sail switch circuit tells the PC board that there is enough CFM of air to open the GAS VALVE and trigger the IGNITOR.
Causes of open sail switch, so nothing but fan runs:
1. Low voltage-- fan turns too slowly
2. Restriction in air return
3. Restriction on outlet side such as crushed hose or too many closed vents.
Start by checking voltage at the house battery and also at furnace when this occurs. 12.7= fully charged battery. 12.2= 50% discharged battery.
Brett