I had a similar problem a couple of years ago. The generator shut-down with a fault light. I reset the fault, and the generator started just fine, but produced no electricity. It turns out the original fault was over-temp because the fan wasn't running due to no juice from the generator.
I took it to a Powertech shop, hoping it was something simple, like a regulator. No such luck. The rotar had a blown winding. After that was fixed (about $2000 later), I left the shop with a running generator, only to return a few minutes later with a stopped generator and a fault light. This happened at least five times before they correctly located and solved the problem.
At first they thought the fault was due to low coolant, so they burped the radiator. No luck.
Then they thought it was low oil pressure, do they did an oil change to make sure the correct oil was being used. No luck.
Then they thought the oil pressure sensor was bad and replaced it. No luck.
Then they though the coolant temperature sensor was bad and replaced it. No luck.
Since they ran out of ideas, I looked into the FT docs and found there was a coolant level sensor they did now know about. They replaced it and the problem was solved.
It's been fine ever since.