PowerTech 10KW Runs then Stops

Changing the coolant on my Cummins and while I'm at it planning on changing the coolant in the generator.  I was running the generator and it starts, but continues to die after running for about 4-5 minutes.  Where can I start to debug this?  The service center that did the Cummins oil change also changed the oil, oil filter, and fuel filter on the generator.  I'm wondering if there could be an issue with the fuel filter having air in it or not flowing correctly?
Benjie, Ashley, Zoey, Fallon, and Lake
Round Rock, TX
In search of our next monster...

Re: PowerTech 10KW Runs then Stops

Reply #1
I would start with fuel supply issues.  With a coach that age, the fuel supply line would be my first suspect.  Try running with a fuel supply from a bucket direct from the fuel pump.  If it runs smoothly uninterrupted, the fuel line replacement is in order.
Peter & Beth Martin
No Forrest? What have you done?
MC# 15890 until Dec 2016; FMCA #F329677
Cincinnati, OH

Re: PowerTech 10KW Runs then Stops

Reply #2
I was running the generator and it starts, but continues to die after running for about 4-5 minutes.  Where can I start to debug this?

Any fault lights?  That's usually the best place to start.
Learn every day, but especially from the experiences of others. It's cheaper!  - John C. Bogle

2000 U320 36' non-slide / WildEBeest Rescue
2003 U320

Re: PowerTech 10KW Runs then Stops

Reply #3
And of course we have the handy sticky topic here

Generator Topics Recap
Learn every day, but especially from the experiences of others. It's cheaper!  - John C. Bogle

2000 U320 36' non-slide / WildEBeest Rescue
2003 U320

Re: PowerTech 10KW Runs then Stops

Reply #4
Where would the fault lights be? I'm beginning to think it might be overheating and shutting itself off. Maybe a thermostat?
Benjie, Ashley, Zoey, Fallon, and Lake
Round Rock, TX
In search of our next monster...

Re: PowerTech 10KW Runs then Stops

Reply #5
I sat there and watched.  When it shuts down, there is coolant coming out the overflow and if I pop the petcock on top of the engine (pictured), there is steam that flows out and the hose is very hot to the touch.  The weird thing is the hose coming out of the bottom of the radiator is very cool to the touch.  My guess is something is not allowing the coolant to circulate through the radiator.  Any ideas on culprits or how to debug?  Off the top of my head, could be air bubble, blockage in the radiator or hoses, or thermostat stuck shut?
Benjie, Ashley, Zoey, Fallon, and Lake
Round Rock, TX
In search of our next monster...

Re: PowerTech 10KW Runs then Stops

Reply #6
I had that issue with my unit and it was a loose belt on the water pump/fan pulleys.
Tom and Linda
1995 U280SE #4636

Re: PowerTech 10KW Runs then Stops

Reply #7
There are fault lights on the front of the generator itself.  Sensors that can cause a fault and shut-down the generator included low coolant, high temperature, and low oil pressure. On mine the coolant level and temp are tied to one fault light (which confused the tech greatly, since the over-temp light was lit but the temp was ok) .
Tom Lang K6PG (originally  KC6UEC)
and Diane Lang
2003 38 U295 build 6209
2016 Jeep Grand Cherokee Summit Ecodiesel
still have tow-ready 2006 Acura MDX 
Temple City, California
Motorcade 16681 California Chapter President
SKP 16663 member of SKP Park of the Sierra, Coarsegold California
FMCA F071251
Retired electrical and electronic engineer

Re: PowerTech 10KW Runs then Stops

Reply #8
One more thing, the generator will run even if it is not producing any electricity.  In this case, the cooling fan (electrically driven) will not run, and the generator will shut down for being over temperature.
Tom Lang K6PG (originally  KC6UEC)
and Diane Lang
2003 38 U295 build 6209
2016 Jeep Grand Cherokee Summit Ecodiesel
still have tow-ready 2006 Acura MDX 
Temple City, California
Motorcade 16681 California Chapter President
SKP 16663 member of SKP Park of the Sierra, Coarsegold California
FMCA F071251
Retired electrical and electronic engineer

Re: PowerTech 10KW Runs then Stops

Reply #9
Assuming the radiator fan is workng, antifreeze if up to proper level, I would be thinking thermostat not opening, However in your case I would be looking close at the fan.  We have seen a very strange happening on a Kubota engine, where the engine was running fine but the water pump was not turning very fast, crankshaft pulley was slipping, needed new pulley on crankshaft.  Just a thought on that one, very rare in my world.
A stuck thermostat will eventually make the bottom hose very hot too, why thinking fan issue.
Good luck

Re: PowerTech 10KW Runs then Stops

Reply #10
water pump toast?
fan not running?
The selected media item is not currently available. Dave Head & Megan Westbrook
Titusville, FL - The Great Outdoors
'98 270 buying this month
Toad is a 2018 F150 XLT

Re: PowerTech 10KW Runs then Stops

Reply #11
Sounds like it's shutting down on overheat. I had the same issue with a 95 U320. The generator radiator is mounted vertically. They are prone to air pockets which cause the water pump to cavitate. There should be a small drain valve at the top of the radiator, crack it while the engine's running to allow the air to escape. Make sure to keep the coolant system full.
David Bethard
2003 U320 - 40ft. Build #6159
ISM 500hp
2006 Jeep Liberty CRD
2021 Honda Goldwing DCT

Re: PowerTech 10KW Runs then Stops

Reply #12
I had the same thing with mine (10kw like yours) and it was the fan not coming on like it was supposed to.  The really good news is that the genset cut off.  If it didn't you would be buying an new one.  This generator is designed to cut off when it gets too hot (thank goodness).  If fan is working and blowing well, check the hoses to make sure not kinked and belts intact.  Mine seemed to do that as it slid in and out on the tray. If they are original hoses, I would recommend changing at your earliest convenience. 
Best of Travels

Re: PowerTech 10KW Runs then Stops

Reply #13
I have the same generator on mine. It was the fan, was not going on like it is supposed to do.  Make sure it is on.  If the fan is blowing well, look at the antifreeze, make sure full, I had an issue with the bracket holding the metal support that protected the belt mechanism.  I had to take off and took to a welder to reweld the bracket as it was eating the belts.  Another issue I thought may have been a problem was I was concerned about the rubber coolant hoses, I changed all of them as mine were about 15 years old.  It may not be significant but I was concerned about the hoses kinking when I slid the genset in and out.  I put another larger hose over where I thought the kink would occur and this rounded out the bend so there was no kink.  Since that time all is A-OK.  You may consider changing oil if it overheated too.  I think a good idea. 
Best of Travels

Re: PowerTech 10KW Runs then Stops

Reply #14
Unfortunately, no fault lights that I can find anywhere on my genny. :-(
Benjie, Ashley, Zoey, Fallon, and Lake
Round Rock, TX
In search of our next monster...

Re: PowerTech 10KW Runs then Stops

Reply #15
All, thanks so much for the suggestions.  I was tied up with the coolant change on the Cummins and had to get that done before dark otherwise I'd have been stuck in front of my buddies house!  I don't KNOW FOR SURE that it's overheating, but that is my guess given the steam from the petcock on top of the thermostat and radiator cap.  I have a few questions WRT to your feedback...

1. The pic I posted of the petcock and what I'm assuming is the thermostat housing (correct?), is that hose the supply to engine or return to the radiator?  It was hot to touch and the hose coming out of the bottom of the radiator wasn't even warm.  Depending on the direction of water flow, that could possibly tell me something.

2. I'm a little confused on the radiator fan, belt, etc.  It seems some of you imply that if the belt is slipping the radiator fan might not be cooling?  My radiator is housed in a separate compartment and there is what looks to be an electric fan in that compartment that is for cooling the radiator.  I can tell you that, that fan is kicking on.

3. So, what does the genny belt turn?  Just the water pump or is there another fan behind that big shield?

4. How do I pull the shield off the side of the generator.  I took a brief look and only saw two bolts, one looks to be part of the thermostat housing and the other is on a bracket.  Is that it or is there one hiding behind?

5. I would also like to note, that the radiator hoses seem to be in good shape and fairly new.  Don't look to be 15 years old IMHO.

"A stuck thermostat will eventually make the bottom hose very hot too, why thinking fan issue." - I was thinking about this.  The first time I started it, it may have run for 10 minutes.  The next time only 5 min.  If the thermostat is stuck close but the cooling fan is running properly, I would think it would take some time to heat the water at the opposite end?  I'm a newbie at this so feel free to poke holes in this logic also, it really depends on the coolant flow direction which I'm not sure how it flows.
Benjie, Ashley, Zoey, Fallon, and Lake
Round Rock, TX
In search of our next monster...

Re: PowerTech 10KW Runs then Stops

Reply #16
I still suspect the fuel lines.  If you start the genset tomorrow and it runs for 10 mins. then cuts off.  Try to start it in 5 minis and see hoe long it runs.  Once the fuel in the lines gets consummed, you start to get air into the fuel being injected to the cylinders.  Try the fuel supply from a bucket with a hose from the suction side of the fuel pump.  This way you can definitely rule out the fuel supply.
Peter & Beth Martin
No Forrest? What have you done?
MC# 15890 until Dec 2016; FMCA #F329677
Cincinnati, OH

Re: PowerTech 10KW Runs then Stops

Reply #17
Peter, I'm only hesitant to do this because there was some serious steam coming out of the petcock when I opened it and the coolant expanded enough to start flowing out of the overflow. If it was a fuel problem, I wouldn't think the coolant would get hot enough to create that kind of steam since it should only be about 190 degrees?

I don't mind trying this to see if its the issue, but I'm also concerned about running the engine too much if the problem is overheating. Can't be too good for it. Thinking I may try changing the thermostat, check/tighten the belt, then bleed the radiator first. If that doesn't fix the problem, move on to fuel as that is the lesser of two evils.
Benjie, Ashley, Zoey, Fallon, and Lake
Round Rock, TX
In search of our next monster...

Re: PowerTech 10KW Runs then Stops

Reply #18
I agree.  If the engine overheats in just 10 minutes, then there is no coolant flow through the radiator.  Then it's pump, thermostar, belt (if applicable).  The board & temp. sensor seem okay it it's cutting-off fuel supply on overheat detection.
Peter & Beth Martin
No Forrest? What have you done?
MC# 15890 until Dec 2016; FMCA #F329677
Cincinnati, OH

Re: PowerTech 10KW Runs then Stops

Reply #19
I was thinking about some of this last night as I was going to bed.  I was on a slight incline on the street, in fact I tried leveling and the HWH gave me an excessive slope warning.  I guess its possible that an air pocket could have formed causing the pump to cavitate.  Anyone know about the following...


1. The pic I posted of the petcock and what I'm assuming is the thermostat housing (correct?), is that hose the supply to engine or return to the radiator?  It was hot to touch and the hose coming out of the bottom of the radiator wasn't even warm.  Depending on the direction of water flow, that could possibly tell me something.

2. I'm a little confused on the radiator fan, belt, etc.  It seems some of you imply that if the belt is slipping the radiator fan might not be cooling?  My radiator is housed in a separate compartment and there is what looks to be an electric fan in that compartment that is for cooling the radiator.  I can tell you that, that fan is kicking on.

3. So, what does the genny belt turn?  Just the water pump or is there another fan behind that big shield?

4. How do I pull the shield off the side of the generator.  I took a brief look and only saw two bolts, one looks to be part of the thermostat housing and the other is on a bracket.  Is that it or is there one hiding behind?
Benjie, Ashley, Zoey, Fallon, and Lake
Round Rock, TX
In search of our next monster...

Re: PowerTech 10KW Runs then Stops

Reply #20
Is this an Isuzu engine?
Peter & Beth Martin
No Forrest? What have you done?
MC# 15890 until Dec 2016; FMCA #F329677
Cincinnati, OH

Re: PowerTech 10KW Runs then Stops

Reply #21
Kubota

Best Regards,
Benjie

Benjie Zeller
(512) 587-4628
Benjie, Ashley, Zoey, Fallon, and Lake
Round Rock, TX
In search of our next monster...

Re: PowerTech 10KW Runs then Stops

Reply #22
Not familiar with the Kubota, so not sure about the set up.  Mine is a PT 8 KW with Isuzu, and the radiator is mounted with the engine along the sliding tray.  Not a great set up due to vibration.
Peter & Beth Martin
No Forrest? What have you done?
MC# 15890 until Dec 2016; FMCA #F329677
Cincinnati, OH

Re: PowerTech 10KW Runs then Stops

Reply #23
We have the 10K PowerTech with Kubota engine. The radiator fan is electric and is located in the small bay below the drivers seat. The fan blows air through the radiator at the rear of the bay and it is exhausted out the back of the bay near the driver side tire. The air is deflected away from the tire toward the passenger side.

One time I turned a switch off at the control box on the generator to see what would happen. The generator shut down in about five minutes. The switch controlled the electric fan. If the fan is not blowing copious amounts of air through the radiator and exhausting it under the coach, the generator will shut down quickly.
J D Stevens
1997 U295 CAI 36' Build #5085
2002 Subaru Outback
Motorcade 16869
Bellville, TX

Re: PowerTech 10KW Runs then Stops

Reply #24
Benjie,

You have not confirmed that the generator is indeed making AC power.  Is it?  Also, have you bled the petcock at the top of the generator radiator? 