Re: Generator Fuel Lines
Reply #1 –
A couple of years ago I had a generator fuel line leak. I replaced the lines with the same expensive lines that FT installed. If I had it to do over, I would use just a good fuel line approved for diesel. It doesn't make sense not to replace both lines at the same time. I worked backwards from the generator as it is easy to tell which is which at the generator. I think it took 32 ft of hose, but my diesel tank and propane tank locations are reversed as compared to your coach, so you may need less hose. It wasn't easy getting to the pipe fitting in the middle of the tank. You need what is called a crow foot flarenut wrench on an extension to remove the fitting. A set at Harbor Freight is $12. The hose that FT used just pushes on to a barbed fitting designed to work with that hose, but the hose has to be sliced lengthwise to remove it. Be careful not to damage the barbed fitting when cutting the hose. Another type of hose might not work with the barbed fitting. Trying to think of the name of the hose, Aeroquip socketless, just looked it up. I posted about doing it.