No Generator power to transfer switch

Instead of 120VAC; meter reading 8.5- 10 vac going to the 45 amp circuit breakers; and the same going to the fan circuit breaker.  However, fan is not running at all.  Generator starts and runs OK.
Fiddler
1959 Parris Island grad
40' 2001 U320 Build 5875
1999 Suburban K1500 toad
1986 Corvette Pacecar
ssoftail@comcast.net

Re: No Generator power to transfer switch

Reply #1
There has been a thread on this subject before. Try doing a search.
2014 ih45  (4th Foretravel owned)
 1997 36' U295 Sold in 2020, owned for 19 years
  U240 36' Sold to insurance company after melting in garage fire
    33' Foretravel on Dodge Chassis  Sold very long time ago

Re: No Generator power to transfer switch

Reply #2
On the voltage regulator, locate the F+ and F- wires, mark to keep clear which is which, using a 9 volt transistor battery, while running the engine connect the battery and read the generator output voltage, no load, breakers off including the fan.  Voltage should read about 100 volts.  If so, you need a regulator, if no or very low reading, you need to remove generator to determine if it is the rotor or stator issue.
With your reading of 8-10 volts would normally indicate the regulator issue.
  Very simple