Re: Ground fault outlet went.
Reply #5 –
Pat,
If the circuit breaker for the garage trips you may have another problem than the GFI. Does the garage breaker stay closed with nothing plugged in and is there nothing else on that circuit? If it stays closed with nothing plugged in, I suggest you open all the breakers in the coach, plug it in and see if it trips. If okay close the main breaker, and then close all the other breakers one at a time until you find the problem. A tripped GFI should not have anything to do with the garage breaker. The breaker the GFI is on would only trip for an overload, not a ground fault. Make sure nothing is plugged into the outlets downstream from the GFI and there is probably some of those outlets in the lower bays or on the outside of the coach. Maybe a TV or something is plugged into one of those outlets. A defective appliance can trip the GFI.