Topic: Furnace ignites but cool air comes out of ducts (Read 947 times) previous topic - next topic

Furnace ignites but cool air comes out of ducts

I have a 1986 Grand Villa. When I turn the front furnace on the fan blows cold air through the ducts at a reasonable rate but when the furnace ignites, the air-flow diminishes and only cool air comes out of the ducts.  I am 99% certain that there are no blockages in the 3 separate ducts.  The fan speed does not appear to change after the furnace ignites.

Any ideas?
Marty Day
1986 GV 36'

Re: Furnace ignites but cool air comes out of ducts

Reply #1
Marty, my guess is that the furnace ignites but then the flame goes out within a few seconds. It will keep blowing. If the sail switch or any of the other functions do not send the right signal to the control board, the board kills the gas flow. You also may need to get the gas pressure checked. If the gas pressure is incorrect, bad regulator, the gas will shut off after initial ignition.
The selected media item is not currently available.Kent Speers
Locust Grove, OK
1993 U300 SSE 40' (Restored at FOT 2009) Build 4323
720 watts Solar
6V92TA DDEC Silver Engine
2014 Subaru Outback

Re: Furnace ignites but cool air comes out of ducts

Reply #2
Well diagnosed Kent. Thermocoupler.
1994 U280, Build 4490
Deming, NM.

Re: Furnace ignites but cool air comes out of ducts

Reply #3
"Air flow diminishes" is the key here. Less air flow means the sail switch opens, so the PC board does NOT open/or keep open the gas valve.

I would start by checking voltage at the furnace PC board.  If 12.5 or more, then look for restrictions in air return or closed vents.
Brett Wolfe
EX: 1993 U240
Moderator, ForeForum 2001-
Moderator Diesel RV Club 2002-
Moderator, FMCA Forum 2009-2020
Chairman FMCA Technical Advisory Committee 2011-2020

Re: Furnace ignites but cool air comes out of ducts

Reply #4
Marty ,
Just to be sure it's not a bad connection, unplug and replug the connector on the control board. Do that three or four times to wipe the connections.
Do the same on any other connections you can get to on that furnace.
JD.
John Duld
1995 U320C SE 40'

Re: Furnace ignites but cool air comes out of ducts

Reply #5
I had a similar problem with my furnace 4-6 years ago and about drove me crazy and everything I did as a cure, was a failure. 
I finally, after a LOT of further investigation found that Mud Dauber wasps had built TWO of their famous nests inside the burner tube.  I had found the first one most outboard) but missed the fact that they built another nest AROUND THE CORNER IN THE TUBE, where I was unable to see it without a long handled mirror and a high powered flashlight.  Used my battery drill and a piece of cable to tear up the next and then blew it out.
Furnace fired right up after that.
You just never know what you are gonna find inside tubes. 
Same thing happened to my air horns.
Regards,
JON TWORK KB8RSA
Full Time RVer (10+ Years) & Dedicated Boondocker
Retired, Unemployed, Homeless Transients
1996 Foretravel U270-36 w/24' Timberwolf Trailer
I firmly believe that tomorrow holds the possibility for new technologies, astounding discoveries, and a reprieve from my remaining obligations.
Welcome to WeRV2 (Under Construction)
Find Jon: Via Satellite Tracker Datastorm Users
The Second Amendment is in place in case they ignore the others.

Re: Furnace ignites but cool air comes out of ducts

Reply #6
One other little trick after checking all of the electrical connections is that if you coach has two furnaces the chances are they both use the same control board. I have taken the control board out of the one that works and put it in the one that isn't working to see if it is the board or not. If the board fixes the problem  you know you need a new board. If not you can move on to other problems like the mud dobbers in the burner or a bad or corroded sail switch.
The selected media item is not currently available.Kent Speers
Locust Grove, OK
1993 U300 SSE 40' (Restored at FOT 2009) Build 4323
720 watts Solar
6V92TA DDEC Silver Engine
2014 Subaru Outback

Re: Furnace ignites but cool air comes out of ducts

Reply #7
@Marty since you have an older coach you might want to check for oil in the LP line. See this post for more info.

LP Maintenance

see ya
ken
The selected media item is not currently available.ken & dori hathaway & Big Agnes
🍺1992 U300 GrandVilla WTBI #4150 FOT FBP 2011
✨6V-92TA DDEC Parlor Coach 350HP Series 92
🏁2011 Nissan XTerra Pro-4X

Re: Furnace ignites but cool air comes out of ducts

Reply #8
Thank you all for your suggestions.  Kent, you are correct in that the furnace ignites for between 3 and 4 seconds and then goes out (the rear furnace and the stove work perfectly).  Now I have to try to reach the electrics which are hidden behind 2 tightly-packed duct hoses.  I am beginning to wonder if the coach was built around the furnace, lol.
Marty Day
1986 GV 36'

Re: Furnace ignites but cool air comes out of ducts

Reply #9
Marty, the electronics on my coach's furnaces are on the left hand side of the furnace enclosure. Once you open the outer door they should be in a black or gray plastic box on the left wall. Open the box and take the electronic board out of the back furnace and install it in the front furnace and see if works. If that doesn't fix it then you need to start checking the gas pressure at the furnace. In my 93. U225 there were two gas regulators, one for the front furnace and one for the back. My symptoms were just like yours but it was the back furnace that wouldn't stay lit. It was a bad regulator and nothing to do with the furnace. I found that out by spending over $200 at Camping World for nothing. Then I found a certified Atwood tech at a local RV dealer. He used a water column to check the gas pressure and then fixed it in 20 minutes and a cost of $45 for a new regulator.

Hope this helps.
The selected media item is not currently available.Kent Speers
Locust Grove, OK
1993 U300 SSE 40' (Restored at FOT 2009) Build 4323
720 watts Solar
6V92TA DDEC Silver Engine
2014 Subaru Outback

Re: Furnace ignites but cool air comes out of ducts

Reply #10
I have checked a few things.  With the furnace switched off at the wall thermostat there are 13.2 volts at the circuit-breaker on the furnace.  When the blower starts up, the voltage at the circuit-breaker drops to 12.2 volts and the voltage from the sail switch at the relay is 10.4 volts.  When the burner ignites, the voltage from the sail switch drops to 9.4 volts.  When the burner goes out after ~ 4 seconds, the voltage from the sail switch reverts to 10.4 volts.  The burner ignites 3 times whereafter a red light flashes on the circuit board.  I cannot actually see the sail switch but I assume that the burner would not ignite at all if it were malfunctioning.

I have not tried switching the circuit boards (from the rear furnace).  I gave the rear board a cursory inspection and it looks different to the front one.  I shall continue scratching my head.
Marty Day
1986 GV 36'

Re: Furnace ignites but cool air comes out of ducts

Reply #11
Marty,

That is way too much voltage drop-- assuming voltage at the battery stays steady at 13.2.  At most, repeat most, you should loose 1.0 VDC.  If more, check connections.  Worse case, blow $15 and power the furnace using a relay and fuse with heavier gauge wire from better source of power.
Brett Wolfe
EX: 1993 U240
Moderator, ForeForum 2001-
Moderator Diesel RV Club 2002-
Moderator, FMCA Forum 2009-2020
Chairman FMCA Technical Advisory Committee 2011-2020

Re: Furnace ignites but cool air comes out of ducts

Reply #12
Thank you, Brett.  I was pretty sure that there should not be such a drop in voltage.  I shall clean all the connections that I can get to and see if there is any improvement.
Marty Day
1986 GV 36'

Re: Furnace ignites but cool air comes out of ducts

Reply #13
Hi Marty,

From the dropping voltages with more furnace parts turning on...it might be a poor ground. Some circuit boards donot function well at less than about 11 volts.
Jim Frerichs
2002 U320 42'

Re: Furnace ignites but cool air comes out of ducts

Reply #14
Absolutely check the ground side as well as positive side.  No problem running an additional ground wire to clean bare metal on the frame.
Brett Wolfe
EX: 1993 U240
Moderator, ForeForum 2001-
Moderator Diesel RV Club 2002-
Moderator, FMCA Forum 2009-2020
Chairman FMCA Technical Advisory Committee 2011-2020

Re: Furnace ignites but cool air comes out of ducts

Reply #15
SUCCESS!  Well it's working now.  I removed the plug on the circuit board and as I was fiddling with it, it came apart into 2 separate and distinct pieces.  I cleaned it up (although it looked clean) put it back together, plugged it back in, switched the furnace on and - Hey Presto! - it ran and ran. 

Thank you all for your kind help.  So often it is something simple.

It is darn hot in here! ^.^d
Marty Day
1986 GV 36'

Re: Furnace ignites but cool air comes out of ducts

Reply #16
Oh dear.  I spoke too soon.  The furnace worked fine for several hours then reverted to the same fault.  The outside temperature is below 40 so I shall try to check for any oil in the line as Ken suggested.
Marty Day
1986 GV 36'

Re: Furnace ignites but cool air comes out of ducts

Reply #17
Marty,
If moving the connector on the control board made it work for awhile I would concentrate on that plug and the wires that feed that plug.
Also look carefully at the board where the plug connects to the board.
It's not likely a propane supply problem would fix it's self then fail again.
John Duld
1995 U320C SE 40'

Re: Furnace ignites but cool air comes out of ducts

Reply #18
Check voltage again when symptoms reappear.
Brett Wolfe
EX: 1993 U240
Moderator, ForeForum 2001-
Moderator Diesel RV Club 2002-
Moderator, FMCA Forum 2009-2020
Chairman FMCA Technical Advisory Committee 2011-2020

Re: Furnace ignites but cool air comes out of ducts

Reply #19
I gave some logical thought to my problem.  The furnace ignites thus the blower, sail switch, relay and those parts of the CB must be working - for a short time at least.  So, I thought, what is required to keep the furnace going.  Answer: the heat sensor.  So I took it out, cleaned it (although there were no heavy deposits), squeezed the connector on the wire a bit, refitted it and so far the furnace has worked.  Fingers and everything else crossed.
Marty Day
1986 GV 36'

Re: Furnace ignites but cool air comes out of ducts

Reply #20
Occam's razor!

Brilliantly applied.
Tom Lang K6PG (originally  KC6UEC)
and Diane Lang
2003 38 U295 build 6209
2016 Jeep Grand Cherokee Summit Ecodiesel
still have tow-ready 2006 Acura MDX 
Temple City, California
Motorcade 16681 California Chapter President
SKP 16663 member of SKP Park of the Sierra, Coarsegold California
FMCA F071251
Retired electrical and electronic engineer