Re: 2014 Ladies Driving School - Tech Seminar
Reply #18 –
I don't expect my Prosine inverter/charger to operate differently than anyone else's. It is programmed to limit current or limit voltage according to a "smart" algorithm.
One you are fully charged, it goes into float mode, keeping the battery voltage at 13.5 until something changes.
If the battery is discharged when you plug in, it goes into Bulk mode first, charging at constant current (107A on mine) until the voltage rises to 14.4v, at which time the battery is 75% charged. Then it goes into Absorption mode, where the voltage is held at a constant voltage (14.0 - 14.8 volts depending on temperature), during which time the current decreases as the battery charges. The charger switches from Bulk to Float, a constant 13.5 volts, when the battery is fully charged, and stays there indefinitely. I don't know if the switch from Bulk to Float is because of time or because the current is below a preset threshold.
The important thing to remember, is that the charger is designed to put out it's maximum rated current, and it will not out any more. If it was at float when you closed the boost switch, it might switch to Absorption if the chassis batteries are low, or it might stay at Float. But when you start the starter with the boost switch on, it will see a drop in battery voltage, which might trigger Absorption mode, sending that current wherever needed.
Don't worry, the charger is designed to put out 100A, whether to one or two banks of batteries, or the engine and starter. Amps is Amps.
By the way, this kind of circuit is usually protected by time delays, so a sudden load would need to be present for some amount of time before the charger will switch modes.