Re: Partial electrical power loss
Reply #12 –
If...IF yours is kinda wired like my much older unit, you have 2 heavy wires going from the buss (1 each leg) to a transfer switch (no. 2), no breaker on this line. This feed is from both shore and generator, determined by the main transfer switch (no.1). Each inverter is feeding the other side of that transfer switch (no.2)....again no breaker. The output from that xfer switch feeds the inverter sub-panel. That panel is protected by one breaker, probably a double in your case. I'd look at transfer switch no.2, maybe try some persuasive percussion on it? This is ALL speculation on my part, not knowing your system, or having access to the drawings makes it all a crap shoot. Surprised that James could help though.
One added question, which you MAY have answered, do you have the problem when running on the inverters ?