Re: Question for Inverter Gurus: Passthrough vs. Direct Inverter Load
Reply #14 –
Interesting discussion. Our coach has been modified from original factory equipment. First, I removed our generator/shore power ATS and replaced it with a manual switch. Second, when AM Solar installed our Magnum MS2812 inverter, they said the inverter's internal pass-thru relay could replace the coach's inverter ATS, so it was also removed. We have been operating without any ATS box for 2 years now, and everything seems to work fine. The inverter has never shut down for any reason while in pass-thru mode. I have never made any attempt to limit the AC load in this mode, because I was under the impression that the only restriction would be the 50 amp breaker at the power pole (or the breaker on the generator).
But now this discussion has me wondering if we are indeed limited to 30 amps of current draw when the inverter is in pass-thru mode. I looked up the page showing the inverter 30 amp circuit breaker in the Magnum MS Inverter owner's manual. The whole page is linked below in .pdf format. There are two paragraphs pertaining to the 30 amp circuit breaker, which I have copied below:
"AC Input Circuit Breaker (CB3) – this circuit breaker protects the unit's internal charger wiring and pass-thru relay while in Standby mode. The circuit breaker pops out when it opens—press in to reset. The input circuit breaker is not branch-rated, therefore branch-rated circuit breakers must be installed in the inverter's input wiring."
"CAUTION: The inverter's internal AC transfer relay is rated for 30 amps per leg. The pass-thru current must be no greater than 30 amps per leg or damage to the relays may occur."
So does that CAUTION note mean I can only pull a total of 30 amps through the inverter in pass-thru mode, OR can I pull a (theoretical) total of 60 amps (30 amps + 30 amps), in which case the power pole (or generator) 50 amp breaker would control the load? I'm not a electrician, so this stuff gets over my head pretty quickly.
Believe the 30 amps per leg refers to two 30 amp circuits. Does not mean they can supply 60 amps. My inverter panel has a 50 amp input breaker and three 20 amp output breakers, so I can only supply 50 amps total before that breaker trips.
Check the wiring to the inverter/charger, doubt it is 50 amps. Pass through power is limited to whatever is supplied to the inverter from the main breaker panel. Power to my inverter from main panel is on a 30 amp breaker, so my max pass through can only be 30 amps. Yours may have been rewired, but the reason Foretravel installed the bypass ATS was because of the 30 amp limitation on the inverter relay.