Topic: Generator fan capacitor question (Read 1219 times) previous topic - next topic

Generator fan capacitor question

Kubota shut down during our exercise run yesterday and the "High Temp" indicator light was activated.  Run time was about 10 mins.

Started the genset this AM and found that the cooling fan was not turning.  I removed the screws holding the cover plate on and moved the squirrel cage with my finger and it began to spin and the Kubota ran for 30 mins.  My understanding is, if a 110 VAC motor has trouble starting it would point to a capacitor problem.  Usually the capacitor is mounted to the motor.  Not on this one.

Does anyone know where the capacitor is located and/or do I need to replace the motor.

I called Avery at MOT this AM and he advised that the capacitor is on the motor housing and should be replaced without pulling the motor.  I do not see a capacitor anywhere. 

I also called Power Tech but have not heard back from them.

Thought I would check here before I call Avery back again.

Checked oil - OK
Checked Coolant - added some to overflow bottle
Engine coolant supply and return hoses are hot -
Breakers all appear to be OK

Thanks in advance for your thoughts.  :D


Scott & Carol Seibert
2001 42' double slide U320 - Sold
Previous - 2002 36' U320

Re: Generator fan capacitor question

Reply #1
Scott, you are correct.  Replace the start capacitor. You can take it out and test it with a meter. You can find the procedure on google. On one of our Foretravel Rallies one individual had to get to his capacitor from underneath.
John & Carm Morales

"We travel not to go anywhere, but to just go.  We travel for travel's sake.  Our great desire is to move."

Re: Generator fan capacitor question

Reply #2
Thanks John.  Got to find the dern thang first.  :D
Scott & Carol Seibert
2001 42' double slide U320 - Sold
Previous - 2002 36' U320

Re: Generator fan capacitor question

Reply #3
Crawl underneath.  That is where one member found it.  Can't be seen from above.
John & Carm Morales

"We travel not to go anywhere, but to just go.  We travel for travel's sake.  Our great desire is to move."

Re: Generator fan capacitor question

Reply #4
Kubota shut down during our exercise run yesterday and the "High Temp" indicator light was activated.  Run time was about 10 mins.

Started the genset this AM and found that the cooling fan was not turning.  I removed the screws holding the cover plate on and moved the squirrel cage with my finger and it began to spin and the Kubota ran for 30 mins.  My understanding is, if a 110 VAC motor has trouble starting it would point to a capacitor problem.  Usually the capacitor is mounted to the motor.  Not on this one.

Does anyone know where the capacitor is located and/or do I need to replace the motor.



I called Avery at MOT this AM and he advised that the capacitor is on the motor housing and should be replaced without pulling the motor.  I do not see a capacitor anywhere. 
I also called Power Tech but have not heard back from them.

Thought I would check here before I call Avery back again.

Checked oil - OK
Checked Coolant - added some to overflow bottle
Engine coolant supply and return hoses are hot -
Breakers all appear to be OK

Thanks in advance for your thoughts.  :D



Look in a J box directly above the blower, mine [03] is in that box. The fact that it will start spinning when you turn the blower wheel could very well indicate the start cap.
Jim C.
coachfree, previous 1997, 1999, 2000, and 2003 Foretravels.

Re: Generator fan capacitor question

Reply #5
My capacitor is inside the junction box above the fan. Have an 03 so may be different
Richard & Betty Bark & Keiko our Golden Doodle
2003 U320T 3820 PBDS
Build # 6215
MC # 16926
2016 Chevrolet Colorado 4X4 diesel

Re: Generator fan capacitor question

Reply #6
I have an '00 U320 and the capacitor is not in the junction box above the fan in my coach.  You may have followed my fan problems recently.  One of the first things I did was test the fan motor by disconnecting the wires from the generator at the aforementioned junction box and connecting it to an appliance cord (from an old washer) and plugged it into an outlet on the side of our house with an extension cord.  When I did this, I found the fan worked well and the issue was no power from the generator.  I also posted a photo of the wiring to the fan and where it connected inside the control box on top of the generator.  A lot of discussion regarding capacitors preceeded our finding the wiring problem.  If your fan runs fine using your house current, there should not be a problem with the capacitor, if I'm not mistaken.  I'm guessing you have a loose wire.  If so, it could be in either of the two junction boxes (one behind the generator up high) or in the control box.  You can PM me if you have any questions along this line.
2000 U320 mid entry  #5688
2006 Jeep Liberty


USMCR retired
SDFD retired
FEMA US&R TF8

Re: Generator fan capacitor question

Reply #7
Thanks for the comments.  Will see if I can find that thing. 

Sven - will try your test and see what I get.
Scott & Carol Seibert
2001 42' double slide U320 - Sold
Previous - 2002 36' U320

Re: Generator fan capacitor question

Reply #8
On my fan the capacitor is mounted to the back side of the fan housing.  I need to slide out the generator, crawl up behind the generator and look back at the rear of the fan.  Voila!
Regards,
Brett

'99 42' Foretravel Xtreme
'14 Brown Motorsports Stacker
'05 Chevy SSR
'02 BMW R1150R

Re: Generator fan capacitor question

Reply #9
Argh.
Scott & Carol Seibert
2001 42' double slide U320 - Sold
Previous - 2002 36' U320

Re: Generator fan capacitor question

Reply #10
Mine (1998) is right on front of the blower as you open the door to the bay.  Sorry that yours is harder to find.

Also make sure the 15(?) amp breaker for the fan is good.
1998 U320 40'
2005 GMC Yukon
MC# 17609

Re: Generator fan capacitor question

Reply #11
I replaced temp sensor and it kept running on Powertech 8k. Interesting what shuts them down.
99 U270. Found belt loose adjusted that also with help of friend with long screwdriver while I tightened belt from underneath and behind.
99 40' U270 #5574
2010 Honda Element
Hot Springs Village, AR.
K5IIK

Re: Generator fan capacitor question

Reply #12
Been raining today.  Will look closer tomorrow.

Belt is tight and fuse is good.

Scott & Carol Seibert
2001 42' double slide U320 - Sold
Previous - 2002 36' U320

Re: Generator fan capacitor question

Reply #13
Mine (1998) is right on front of the blower as you open the door to the bay.  Sorry that yours is harder to find.

Also make sure the 15(?) amp breaker for the fan is good.

If anyone needs to replace the circuit breaker, you can get them at Graingers for a couple  of dollars; if you got to Power Tech, it will cost close to $50.
2000 U320 mid entry  #5688
2006 Jeep Liberty


USMCR retired
SDFD retired
FEMA US&R TF8

Re: Generator fan capacitor question

Reply #14
Found the capacitor.  Located attached to the fan housing - way behind and up.  Took a long heavy screwdriver and loosened the fastening strap allowing the capacitor to slide up out of the strap.  Upon inspection, one wire was not connected.  Corrosion ran supreme.  PN 97f9121.  Ordered a replacement from Amazon.  Will mount the new one in an accessible place.

More to come.
Scott & Carol Seibert
2001 42' double slide U320 - Sold
Previous - 2002 36' U320

Re: Generator fan capacitor question

Reply #15
Pic of top of our capacitor.
Scott & Carol Seibert
2001 42' double slide U320 - Sold
Previous - 2002 36' U320

Re: Generator fan capacitor question

Reply #16
Ouch
1999 40 ft. U-320 wtfe build 5563 Chuck & Lynda's "Rollin' Inn"  2030 watts solar
prev. mh's 71 GMC 5 yrs. 73 Pace Setter 1 yr. 78 Vogue 5 yrs 81 FTX 40ft all electric 18 yrs. 1996 Monaco Signature 3 yrs.
2014 Grand Cherokee Overland
Dream as if you will live forever. Live as if you will die today.  James Dean

Re: Generator fan capacitor question

Reply #17
My new capacitor is arriving today and will install in a new location.

Just wondering - Can I cover the connectors with something like silicone to protect the connections from moisture?
Scott & Carol Seibert
2001 42' double slide U320 - Sold
Previous - 2002 36' U320

Re: Generator fan capacitor question

Reply #18
Dielectric grease should be sufficient. See if any other replies have a better idea.
1999 40 ft. U-320 wtfe build 5563 Chuck & Lynda's "Rollin' Inn"  2030 watts solar
prev. mh's 71 GMC 5 yrs. 73 Pace Setter 1 yr. 78 Vogue 5 yrs 81 FTX 40ft all electric 18 yrs. 1996 Monaco Signature 3 yrs.
2014 Grand Cherokee Overland
Dream as if you will live forever. Live as if you will die today.  James Dean

Re: Generator fan capacitor question

Reply #19
You could but a gob of dielectric grease will protect and waterprrof them just as well.
Roger Engdahl and Susan Green
2001 U320 3610 #5879 (Home2) - 2014 Jeep Cherokee or 2018 F150
Hastings, MN

Re: Generator fan capacitor question

Reply #20
 ^.^d  Thanks
Scott & Carol Seibert
2001 42' double slide U320 - Sold
Previous - 2002 36' U320

Re: Generator fan capacitor question

Reply #21
My new capacitor is arriving today and will install in a new location.

Just wondering - Can I cover the connectors with something like silicone to protect the connections from moisture?

There are two different types of silicone. One kind ( I think the one that smells like vinegar, but not positive`) does not do a good job with electric connections
2014 ih45  (4th Foretravel owned)
 1997 36' U295 Sold in 2020, owned for 19 years
  U240 36' Sold to insurance company after melting in garage fire
    33' Foretravel on Dodge Chassis  Sold very long time ago

Re: Generator fan capacitor question

Reply #22
Check with Mouser electronics or Allied electronics for Capacitor boots.

The selected media item is not currently available.Bill&Doris 97 U270 36'
University of Parris Island Class of 66
Semper Fi  Build# 5174 MC#17094


Re: Generator fan capacitor question

Reply #24
Next question:

There r 2 wires attached to the capacitor,  one is solid red the other is red wth a white stripe. 

Which is + and which is - ?

I will check with NAPA re: silicone seal and maybe just cover with dialectic grease.

Thanx again.  :)
Scott & Carol Seibert
2001 42' double slide U320 - Sold